    water-cooled chiller



    Hi all Im a newbie to chiller,condenser and cooling tower which im currently working in (a building). I hope u peeps could help me out with a couple of qns
    1: I have a multistack chiller that have 6 compressors.how are the cooling tower and condenser and chillers related?
    2 : There are 3 compressors in the chiller that lately seems to have problems. the compressors will trip almost everytime we reset it. What im being told is to press the HP button in the modular and then press reset on the touch-screen sensor. But yet it still trip. The discharge pressure will rise up to 1500kpa and then trip. Then It stated "FAULT --- HP" What should I check?
    Just FYI, before I join the building, I notice there are 2 cooilng towers with 8 cooling tower fan motors in the rooftop, 3 condenser pumps and 3 chill water pumps. Now theres only 3 cooling tower fan motors and 2 chill water pumps that is running.
    ask me if you need me to include anything.cheers!



  2. #2
    Join Date
    Apr 2008
    Location
    Dubai, UAE
    Posts
    16
    Rep Power
    0

    Re: water-cooled chiller

    Hi,

    Question no. 1: I have a multistack chiller that have 6 compressors.how are the cooling tower and condenser and chillers related?

    Cooling tower cools down high pressure gas in the condenser into high pressure condensate. High Condensate in introduced to your chiller evaporator via expansion valve to Low pressure that expands to your evaporator wherein you hot media (water) cool down to the designed duty.

    Question no. 2 : There are 3 compressors in the chiller that lately seems to have problems. the compressors will trip almost everytime we reset it. What im being told is to press the HP button in the modular and then press reset on the touch-screen sensor. But yet it still trip. The discharge pressure will rise up to 1500kpa and then trip. Then It stated "FAULT --- HP" What should I check?

    a. What refrigerant you are using prior to setting of your HP cut-out?
    b. Is their enough water in you cooling tower?
    c. Did you check if their is clogging in your line strainer going to your condenser?
    d. How long do this equipment running, Old or new?

    kr,
    alphi

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: water-cooled chiller

    sounds like a possible cooling water flow issue.

    Inspect the towers: Clean, filled properly, right chemicals in them, good water flow?

    Inspect strainers: Clean, good condition?

    Check pumps: Good berrings, good power, running correct speed?

    Check condensers: Clean, proper flow, head valves set correctly to refrigerant being used, balancing valves correctly set?

    If all is good there, is the Hp switch set in accordance with the refrigerant in use? System free or air or moisture? If so it may have simply aged.

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: water-cooled chiller

    how are the compressors related to eachother,
    is it a pure cascade to build up the total power, or for different circuits???

    how long are the in operation ??


    Ice

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: water-cooled chiller

    first test the flow switch, then test the h-p swich

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: water-cooled chiller

    The fact that there are tower fans off probably means the tower leaving water is down to temperature... yet compressors are cycling on high head. This tells us that the heat is not being transferred between the refrigerant and the water in the condenser.

    Either there is insufficient tower/condenser water flow or the condensers are scaled.

    Does each compressor have it's own condenser?
    Last edited by Gary; 19-10-2008 at 07:18 PM.

  7. #7
    Join Date
    Apr 2008
    Location
    The Netherlands
    Age
    49
    Posts
    67
    Rep Power
    16

    Re: water-cooled chiller

    Well, it seems a realy simple case if you say high pressure en condensor not working on max but that would be too easy.

    Wat is the in and outlet temp. on the condensorwater? what is the delta T.

    And in this case as others mentioned check all filters in your water system.

    My advice, don't try to reset the HP alarm to much before you find anything else.

    Greets,

    Bart

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: water-cooled chiller

    Fir
    Welcome, It may be me being silly but I don't come across many chillers that have HP trips set as low as 1500kpa.
    Is it possible that you have a tired HP switch.
    Or should it really trip at 1500 kpa
    Have you tried a gauge on the system to see what discharge pressure you are actually pulling?
    Grizzly

  9. #9
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: water-cooled chiller

    We deal with Multistackon a regular basis
    The units are modular all tied to a common chilled wated system and a common condneser water system. Since each multistack module uses a brazed plate chillers and condneser sections I would think the condenser sections on misc modules is badly fouled. Multistack sells a clean out system for the condenser units. Check out the site for info.

Similar Threads

  1. water cooled subcooler?
    By star882 in forum Technical Speculations
    Replies: 1
    Last Post: 30-12-2007, 12:21 AM
  2. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  3. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 07:14 PM
  4. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •