    ME MXZ-A26WV - Wind



    Dearest Members of RE.com

    I've been, troubleshooting/fixing, a few MXZ-A26WV multi-split misubishi units.

    I've had the same issues since beggining. These units are installed near sea, they are exposed to high velocity winds, sea salt, rain etc.

    My main problem is that the Power Board, Noise Filter and sometimes Electronic PCBoard are always geting themselves defective. It usually starts with PFC defective due to overcurrent (altough I'venever been able to read any overcurrent issue), and it "spreads" to the other boards.

    I was thinking that this could be possibly due to wind gusts that produce some voltage on the fan motor and it damages the PFC circuit, dou any of you think it's possible?

    Also oxidation has been an issue, the lev coils have o be constantly replaced.


    Any help on this, would be appretiated...



    Regards

    Vitor Caçador



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: ME MXZ-A26WV - Wind

    If the wind blows into the front of the unit then the fan free wheels backwards. Then the unit starts the fan in forward direction & has a problem because the fan is going fast in reverse direction.

    Normally suspect power supply problem if overcurrent & noise filter / power board problems.
    Voltage on the neutral line due to some poor N connection in power supply can cause this type of problems.

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: ME MXZ-A26WV - Wind

    Yep, i had the same problem on a outdoor unit nearby the sea.
    i replaced the complete fan whit motor,and changed it for a electronical one, the motor is inbedded in the blades, and it is more silent than the original ones.easier to start en restart.

    Ice

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: ME MXZ-A26WV - Wind

    Quote Originally Posted by Thermatech View Post
    If the wind blows into the front of the unit then the fan free wheels backwards. Then the unit starts the fan in forward direction & has a problem because the fan is going fast in reverse direction.

    Normally suspect power supply problem if overcurrent & noise filter / power board problems.
    Voltage on the neutral line due to some poor N connection in power supply can cause this type of problems.
    I am located near the ocean also.

    Have numerous problems caused by salt conditions, to printed circuit boards.

    At worst some boards fail after 2 years.

    The best solution is to spray the underside of the boards with a silicone or laquer spray and once dry install them as normal. When installed then spray them again on the side where all the connections are made.

    The units that we have done this to are now running trouble free for at least 5 years.

Similar Threads

  1. compressor for wind powered heat pump
    By tomwol in forum Technical Speculations
    Replies: 32
    Last Post: 12-11-2011, 01:05 PM
  2. Part Wind/ Star Delta
    By reggie in forum Technical Speculations
    Replies: 34
    Last Post: 27-08-2008, 05:47 AM
  3. Sea side wind resistant condensing unit fan
    By samurai in forum Technical Speculations
    Replies: 2
    Last Post: 22-11-2007, 01:47 AM
  4. convection/adsorption wind tunnel
    By duke in forum New Technologies
    Replies: 0
    Last Post: 09-07-2007, 09:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •