    R407c



    What are the repercussions of using R 407C for a medium temperature refrigeration application ? I'm aware of the temperature glide of 6-8K and possible fractionation that happens with this refrigerant. How about design and field issues ?

    Design : Evaporator and Condensor selection - need to oversize ?

    Field : Leakages - how do you manage this ?

    Some air-conditioning manufacturers claim that R 407 C is a very efficient refrigerant because of the glide - the compressor suction 'sees' a higher suction temperature and so does not have to 'work ' as hard as say, if R22 is used. But then in the condensor, the condensing temperature also progressively drops and may approach the ambient - so you may need a higher design condensing temperature - and off goes your efficiency advantage , right ?

    Any views/assistance appreciated ?



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi Bersaga
    407c works well at high temperature ranges. My most recent experience is on water to water heat pumps with 2 deg C evaporation and 52 deg c condensing, with COP in the range of 3.8, so you could say it works well there. Medium temp is proabably alright, but you would have a little both controlling your evaporator flooding and your sution superheat, I would say leading to less than ideal (high) superheats and some reduction in effeciency.
    Regards. Andy

  3. #3
    Join Date
    Dec 2002
    Location
    Malaysia
    Age
    59
    Posts
    86
    Rep Power
    22
    Thanks Andy - but say , on an application that requires -15 C evaporating temp. R407 C has a glide of 6-8 K(or more) at that point. Do I select a TXV rated at -15 evap or look for some sort of average ?

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Have a look at this from Copeland http://www.ecopeland.com/Literature/...0100_Glide.pdf

    Frank

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi Bersaga,
    from reading Frank's Copeland document I would say use Dew point to set the expansion valve and Mid point when selecting compressors and matching capacities.
    Kind Regards. Andy.

Similar Threads

  1. P/h chart for R407c
    By Coolie in forum Technical Speculations
    Replies: 4
    Last Post: 29-05-2011, 06:17 PM
  2. R407C to R404a
    By MaDiNfO in forum Air Conditioning
    Replies: 10
    Last Post: 30-07-2006, 09:34 AM
  3. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM
  4. R407C composition
    By Jai in forum Air Conditioning
    Replies: 4
    Last Post: 01-02-2002, 08:59 AM
  5. R407c
    By Mike Hopkins in forum Refrigerants
    Replies: 7
    Last Post: 14-12-2001, 05:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •