29-05-2008, 04:31 PM #1
Chiller short cycling
Hello
Wondering if a chiller will short cycle if the decoupler is located to close to the chillers primary return.
Thanks
-
29-05-2008, 10:18 PM #2
-
29-05-2008, 10:29 PM #3
Re: Chiller short cycling
That would really depend on how much flow is going through the chiller and how much trough the system. If the first is larger, then yes it will!
A decoupler is used to decouple the waterflow from the chiller and that off the system.
This is used, mostly, when there are more than one chiller on the system
-
29-05-2008, 10:54 PM #4
-
29-05-2008, 11:16 PM #5
Re: Chiller short cycling
Yeah there's 4 chillers in parallel. The chiller closest to the decoupler is short cycling. I've read that decoupler must be at least 10 pipe diameters from return on first chiller. On this system it is only 5 diameters.
But then I read Flow alternates both directions in decoupler. Confused
Never got into water chillers in such depth. But would like to learn and appreciate any help
-
29-05-2008, 11:23 PM #6
Re: Chiller short cycling
Lets say you have four chillers of each 100kW with a design delta T of 6K. Then the flow through either chiller, if it's running or will start running, will be 4 l/s. So if the flow from the decoupler through the building is less then the sum of the flow off the chillers it will short cycle. If the flow through the building is larger then that through the chillers the supply temperature will not get satisfied!
-
29-05-2008, 11:35 PM #7
Re: Chiller short cycling
What would be the most common in your experience?
Higher flow in primary side
or
Higher flow in secondary side
-
29-05-2008, 11:38 PM #8
Re: Chiller short cycling
If you give me the temperature's, I'll tell what happens!
Temps I need are entering and leaving water building side, entering and leaving chiller side and entering and leaving water on each chiller where the pump is running!
-
29-05-2008, 11:55 PM #9
-
30-05-2008, 12:01 AM #10
Re: Chiller short cycling
I won't be able to answer untill monday, I'm off to a festival, Pinkpop,tomorrow! Just post them and I'll have a look!
-
30-05-2008, 04:35 AM #11
Re: Chiller short cycling
The design of the common pipe is critical to the performance of a primary-secondary system. The function of the common pipe is to decouple hydraulically the primary and secondary pumps while still providing thermal interaction. To ensure proper system performance, the common pipe design criteria are:
• The maximum pressure drop in the common pipe should not exceed 1.5 ft
Establish the pressure drop in the common pipe by assuming the flow of the largest resultant pressure drop should not exceed 1.5ft. This is the basis of primary-secondary pumping. Higher friction loss in the common tends to make the primary and secondary pumps act in series, resulting in an induced flow in the system. (This incorporates a safety factor.) Typically, a chiller is usually sequenced on or off any time one half of the flow of the largest pump is achieved. For simplicity of design and installation, the common pipe is often the same diameter as the distribution piping.
• Maximum three pipe diameters of separation between the secondary supply tee and the secondary return tee - A common pipe of this length is more than adequate to eliminate mixing due to excessive return velocity in the secondary return piping. Longer length common pipes may result in an excessive pressure drop greater than 1.5 ft with results as described above.
To read the full article go here:http://www.hvacindia.org.in/journals...article05.html
-
03-06-2008, 10:15 PM #12
-
03-06-2008, 10:22 PM #13
-
04-06-2008, 12:14 AM #14
-
11-06-2008, 03:57 AM #15
Re: Chiller short cycling
I have figured out the decoupler, the back strap thingo on the wifes BRA, its refrigeration related, given the steelie glare and chilled response.
Magoo with sore eye
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
DIY aquarium chiller
By BarraCuda in forum Technical DiscussionsReplies: 18Last Post: 06-10-2010, 11:02 PM -
Compressor short cycling....
By sbessettejr in forum Trouble ShootingReplies: 10Last Post: 02-04-2007, 05:09 PM -
Short Cycling blues & low pressure control switch
By mccoolair@yahoo in forum Supermarket RefrigerationReplies: 14Last Post: 09-04-2006, 09:28 PM -
Walk in Cooler (short cycling)
By Brandon in forum Trouble ShootingReplies: 11Last Post: 05-05-2003, 11:43 AM