Results 1 to 15 of 15
  1. #1
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Chiller short cycling



    Hello

    Wondering if a chiller will short cycle if the decoupler is located to close to the chillers primary return.

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,713
    Rep Power
    46

    Re: Chiller short cycling

    Quote Originally Posted by cmac View Post
    Hello

    Wondering if a chiller will short cycle if the decoupler is located to close to the chillers primary return.

    Thanks
    Hi cmac.
    Silly I know!
    But what is a decoupler?
    Is it some sort of quick release coupling?
    If so why would this affect the chiller?
    Cheers Grizzly

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chiller short cycling

    That would really depend on how much flow is going through the chiller and how much trough the system. If the first is larger, then yes it will!

    A decoupler is used to decouple the waterflow from the chiller and that off the system.

    This is used, mostly, when there are more than one chiller on the system

  4. #4
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Chiller short cycling

    Quote Originally Posted by Grizzly View Post
    Hi cmac.
    Silly I know!
    But what is a decoupler?
    Is it some sort of quick release coupling?
    If so why would this affect the chiller?
    Cheers Grizzly
    It's a bypass line between flow and return on a chilled water system.

    Don't quote me on this though but,

    I think its used to balance the flow between the primary and secondary circuits

  5. #5
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Chiller short cycling

    Quote Originally Posted by Lowrider View Post

    This is used, mostly, when there are more than one chiller on the system
    Yeah there's 4 chillers in parallel. The chiller closest to the decoupler is short cycling. I've read that decoupler must be at least 10 pipe diameters from return on first chiller. On this system it is only 5 diameters.

    But then I read Flow alternates both directions in decoupler. Confused

    Never got into water chillers in such depth. But would like to learn and appreciate any help

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chiller short cycling

    Lets say you have four chillers of each 100kW with a design delta T of 6K. Then the flow through either chiller, if it's running or will start running, will be 4 l/s. So if the flow from the decoupler through the building is less then the sum of the flow off the chillers it will short cycle. If the flow through the building is larger then that through the chillers the supply temperature will not get satisfied!

  7. #7
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Chiller short cycling

    What would be the most common in your experience?

    Higher flow in primary side
    or
    Higher flow in secondary side

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chiller short cycling

    If you give me the temperature's, I'll tell what happens!

    Temps I need are entering and leaving water building side, entering and leaving chiller side and entering and leaving water on each chiller where the pump is running!

  9. #9
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Chiller short cycling

    Quote Originally Posted by Lowrider View Post
    If you give me the temperature's, I'll tell what happens!

    Temps I need are entering and leaving water building side, entering and leaving chiller side and entering and leaving water on each chiller where the pump is running!
    Cheers,

    I'll post them tommorrow

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chiller short cycling

    I won't be able to answer untill monday, I'm off to a festival, Pinkpop,tomorrow! Just post them and I'll have a look!

  11. #11
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Chiller short cycling

    The design of the common pipe is critical to the performance of a primary-secondary system. The function of the common pipe is to decouple hydraulically the primary and secondary pumps while still providing thermal interaction. To ensure proper system performance, the common pipe design criteria are:

    • The maximum pressure drop in the common pipe should not exceed 1.5 ft
    Establish the pressure drop in the common pipe by assuming the flow of the largest resultant pressure drop should not exceed 1.5ft. This is the basis of primary-secondary pumping. Higher friction loss in the common tends to make the primary and secondary pumps act in series, resulting in an induced flow in the system. (This incorporates a safety factor.) Typically, a chiller is usually sequenced on or off any time one half of the flow of the largest pump is achieved. For simplicity of design and installation, the common pipe is often the same diameter as the distribution piping.

    • Maximum three pipe diameters of separation between the secondary supply tee and the secondary return tee - A common pipe of this length is more than adequate to eliminate mixing due to excessive return velocity in the secondary return piping. Longer length common pipes may result in an excessive pressure drop greater than 1.5 ft with results as described above.

    To read the full article go here:http://www.hvacindia.org.in/journals...article05.html

  12. #12
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Chiller short cycling

    Quote Originally Posted by wambat View Post
    The design of the common pipe is critical to the performance of a primary-secondary system. The function of the common pipe is to decouple hydraulically the primary and secondary pumps while still providing thermal interaction. To ensure proper system performance, the common pipe design criteria are:

    • The maximum pressure drop in the common pipe should not exceed 1.5 ft
    Establish the pressure drop in the common pipe by assuming the flow of the largest resultant pressure drop should not exceed 1.5ft. This is the basis of primary-secondary pumping. Higher friction loss in the common tends to make the primary and secondary pumps act in series, resulting in an induced flow in the system. (This incorporates a safety factor.) Typically, a chiller is usually sequenced on or off any time one half of the flow of the largest pump is achieved. For simplicity of design and installation, the common pipe is often the same diameter as the distribution piping.

    • Maximum three pipe diameters of separation between the secondary supply tee and the secondary return tee - A common pipe of this length is more than adequate to eliminate mixing due to excessive return velocity in the secondary return piping. Longer length common pipes may result in an excessive pressure drop greater than 1.5 ft with results as described above.

    To read the full article go here:http://www.hvacindia.org.in/journals...article05.html
    Cheers wambat,

    Better than the info I could find myself

  13. #13
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Chiller short cycling

    Quote Originally Posted by Lowrider View Post
    I won't be able to answer untill monday, I'm off to a festival, Pinkpop,tomorrow! Just post them and I'll have a look!
    Thanks

    Forgot about bank holiday this weekend. Be able to post readings tomorrow

    How did festival go? In bits?

  14. #14
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chiller short cycling

    Quote Originally Posted by cmac View Post
    Thanks

    Forgot about bank holiday this weekend. Be able to post readings tomorrow

    How did festival go? In bits?
    Very nice weather, lots of beer and good bands! Really enjoyed myself!

  15. #15
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Chiller short cycling

    I have figured out the decoupler, the back strap thingo on the wifes BRA, its refrigeration related, given the steelie glare and chilled response.
    Magoo with sore eye

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. Compressor short cycling....
    By sbessettejr in forum Trouble Shooting
    Replies: 10
    Last Post: 02-04-2007, 05:09 PM
  4. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  5. Walk in Cooler (short cycling)
    By Brandon in forum Trouble Shooting
    Replies: 11
    Last Post: 05-05-2003, 11:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •