    Pump Down Cut Off Pressure



    Hi,

    I am interested to know that what should be the correct setting for cut off pressure for pump down cycle.

    As per Copeland bulletin, it should be just below the lowest suction pressure of the system.

    If we set pump down pressure to say 50 PSI and cut in at 70PSI, compressor cycles number of times before it stops.

    50PSI in the system is enough to boil out and raise it back to 70PSI after a little while, this just keep the compressor in cycling mode.

    Too much cycling can also cause oil shortage in the compressor.

    Also, is the cut off pressure different for Scroll compressors v/s semi hermetic?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pump Down Cut Off Pressure

    Personally I would set the cut out pressure at around 25psi in your sort of example.

    I would also ensure that the system has a one-shot pump down cycle to prevent compressor restarts if the pressure rises above the cut in pressure unless there is a start command.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: Pump Down Cut Off Pressure

    Quote Originally Posted by jwasir View Post
    Hi,

    I am interested to know that what should be the correct setting for cut off pressure for pump down cycle.

    As per Copeland bulletin, it should be just below the lowest suction pressure of the system.

    If we set pump down pressure to say 50 PSI and cut in at 70PSI, compressor cycles number of times before it stops.

    50PSI in the system is enough to boil out and raise it back to 70PSI after a little while, this just keep the compressor in cycling mode.

    Too much cycling can also cause oil shortage in the compressor.

    Also, is the cut off pressure different for Scroll compressors v/s semi hermetic?
    Weve had loads of problems with scrolls pumping down , converted them in the end to none pump down.Let me know how you get on please , id be very interested to know

  4. #4
    maher wahbe's Avatar
    maher wahbe Guest

    Re: Pump Down Cut Off Pressure

    you have to set at 25psi and defferetionl should be at least 10psi to aviod compressor restart. the setting also debend for refrigeration type which you are using

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Pump Down Cut Off Pressure

    Hi you need to lower the cut out pressure then . Does the system have start delays timers on the compressor/s as this would stop the short cycling
    Transvestites are men who like to eat, drink, and be Mary.

  6. #6
    Join Date
    Jan 2007
    Location
    Portsmouth
    Age
    60
    Posts
    8
    Rep Power
    0

    Re: Pump Down Cut Off Pressure

    Well done Phil, Compressors need protecting, 10mins/6 starts an hour, if there are no timers recommend to your boss or your customer its a good option. Then as long as your LP is set on a lower setting than your running suction pressure, your fine an dandy. If you have a system that is critical ie "close control" you need then to look at offloading/capacity control devices in place otherwise that close control will be lost.

  7. #7
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Pump Down Cut Off Pressure

    Personally I would not lower the LP cutout below the operation envelope of the compressor! This does cause short cycling and Phill/Taffy are right that this should be corrected with a timer. Te problem with LP cutout being too low is that it causes high discharge temperatures even for a short while. This burns a little oil in the discharge of orbital compressors or valve plates and starts a chain of chemical reactions in the system. If the filters can cope with this depends on how often and how much acids you are producing every time you stop the system ... but it will fail!

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. Pump Pressure
    By clivet in forum Technical Discussions
    Replies: 11
    Last Post: 25-04-2006, 07:09 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •