    Question chiller tripping



    hai,

    my chiller carrier 30-gx298 pro-dialoge plus tripping after 10 minutes on alarm code 101.but this code not in service manual.if expan the display compressor motor high temperatue alarm.motor cooling solinoid is working normally.but motor temp is going high.
    suction=44psig.guyes any idea to solve this problem.



  2. #2
    Join Date
    Jul 2005
    Location
    Southern Hemisphere
    Posts
    9
    Rep Power
    0

    Re: chiller tripping

    change over motor temp sensor on terminal plate to spare sensor and try to get a run. check motor temp via controller liquid should inject at 67 degrees could be short of gas or SCPM module needs new software.

    Alarm breakdown is in controls manual at the back in SCPM sub menu.

  3. #3
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: chiller tripping

    I agree with Groid. This happened to me once and I used the spare sensor which solved the problem.

  4. #4
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: chiller tripping

    very thanks to groid and dimitris for ur suggestions.i recheck the unit.used spare sensor.but problem still persist.when unit is tripping motor temp is 116c.now status is
    saturated discharge temp:50c
    saturate suction temp: 4.7c
    discharge gas temp: 82.4c
    discharge superheat 32.3c
    motor temp: 113c

  5. #5
    Join Date
    Jul 2005
    Location
    Southern Hemisphere
    Posts
    9
    Rep Power
    0

    Re: chiller tripping

    discharge temp is far too high, Carrier control alogorithm injects liquid into motor at 67c I think the motor cooling solenoids are not operating correctly could be a solenoid valve/coil failure or the software needs re-programming by Carrier

  6. #6
    Join Date
    Dec 2007
    Location
    u.k
    Posts
    12
    Rep Power
    0

    Re: chiller tripping

    Does the chiller have a aconomiser some units do some dont.If it does check the operation of the EEV.Is just the one circuit effected or both.What is the ambient temprature.With the discharge superheat so high the circuit will be in overide and not loading up fully.

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Question Re: chiller tripping

    Quote Originally Posted by willow View Post
    Does the chiller have a aconomiser some units do some dont.If it does check the operation of the EEV.Is just the one circuit effected or both.What is the ambient temprature.With the discharge superheat so high the circuit will be in overide and not loading up fully.
    thanks guyes,sorry,i was too late to replay.there is not economizer.site glass shows bubbles as comp unloading and loading.then charged around 45kg r22.then manually unloaded the compressor.but problem still remaining.what is the reason of high discharge superheat?will discharge superheat go up,if eev not working properly?

  8. #8
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: chiller tripping

    chek refrigerant flow, re clean / replace ex.valve

  9. #9
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: chiller tripping

    I'm afraid that particular chiller works with R134A refrigerant. Check to make sure you haven't added the wrong refrigerant.

  10. #10
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: chiller tripping

    Quote Originally Posted by Dimitris View Post
    I'm afraid that particular chiller works with R134A refrigerant. Check to make sure you haven't added the wrong refrigerant.
    sorry for wrong infoused134a.i am going to remove the exv.

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. chiller is tripping.
    By V.ARIAN.SHANKAR in forum Air Conditioning
    Replies: 7
    Last Post: 22-05-2008, 01:29 PM
  4. McQuay chiller tripping
    By moideen in forum Trouble Shooting
    Replies: 1
    Last Post: 09-05-2008, 11:19 AM
  5. Replies: 16
    Last Post: 20-02-2008, 11:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •