28-05-2008, 05:22 AM #1
chiller tripping
hai,
my chiller carrier 30-gx298 pro-dialoge plus tripping after 10 minutes on alarm code 101.but this code not in service manual.if expan the display compressor motor high temperatue alarm.motor cooling solinoid is working normally.but motor temp is going high.
suction=44psig.guyes any idea to solve this problem.
-
28-05-2008, 08:11 AM #2
Re: chiller tripping
change over motor temp sensor on terminal plate to spare sensor and try to get a run. check motor temp via controller liquid should inject at 67 degrees could be short of gas or SCPM module needs new software.
Alarm breakdown is in controls manual at the back in SCPM sub menu.
-
28-05-2008, 04:33 PM #3
Re: chiller tripping
I agree with Groid. This happened to me once and I used the spare sensor which solved the problem.
-
30-05-2008, 06:36 PM #4
Re: chiller tripping
very thanks to groid and dimitris for ur suggestions.i recheck the unit.used spare sensor.but problem still persist.when unit is tripping motor temp is 116c.now status is
saturated discharge temp:50c
saturate suction temp: 4.7c
discharge gas temp: 82.4c
discharge superheat 32.3c
motor temp: 113c
-
31-05-2008, 02:43 PM #5
Re: chiller tripping
discharge temp is far too high, Carrier control alogorithm injects liquid into motor at 67c I think the motor cooling solenoids are not operating correctly could be a solenoid valve/coil failure or the software needs re-programming by Carrier
-
31-05-2008, 10:13 PM #6
Re: chiller tripping
Does the chiller have a aconomiser some units do some dont.If it does check the operation of the EEV.Is just the one circuit effected or both.What is the ambient temprature.With the discharge superheat so high the circuit will be in overide and not loading up fully.
-
20-06-2008, 12:37 PM #7
Re: chiller tripping
thanks guyes,sorry,i was too late to replay.there is not economizer.site glass shows bubbles as comp unloading and loading.then charged around 45kg r22.then manually unloaded the compressor.but problem still remaining.what is the reason of high discharge superheat?will discharge superheat go up,if eev not working properly?
-
21-06-2008, 10:33 AM #8
Re: chiller tripping
chek refrigerant flow, re clean / replace ex.valve
-
22-06-2008, 12:18 PM #9
Re: chiller tripping
I'm afraid that particular chiller works with R134A refrigerant. Check to make sure you haven't added the wrong refrigerant.
-
22-06-2008, 06:02 PM #10
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
DIY aquarium chiller
By BarraCuda in forum Technical DiscussionsReplies: 18Last Post: 06-10-2010, 11:02 PM -
chiller is tripping.
By V.ARIAN.SHANKAR in forum Air ConditioningReplies: 7Last Post: 22-05-2008, 01:29 PM -
McQuay chiller tripping
By moideen in forum Trouble ShootingReplies: 1Last Post: 09-05-2008, 11:19 AM -
Trane chiller tripping on "LOW EVAPORATOR REFRIGERANT TEMP"
By kaon in forum Trouble ShootingReplies: 16Last Post: 20-02-2008, 11:15 AM