    pressure drop and chillers



    When the pressure drop of the water is lower than normal, we usually have a low SST. When the pressure drop is extremely higher than normal, what do you think would happen?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: pressure drop and chillers

    If you are talking about the pressure drop across the evaporator then a higher than normal drop means that there is a blockage.

    If there is a blockage then the quantity of cooled water is reduced and the chance of a frozen evaporator is increased.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: pressure drop and chillers

    Thanks for the response, but I think I didn't make myself understood. What I meant was if the water flow was higher than normal, would there be any problems in the refrigeration circuit.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: pressure drop and chillers

    With a higher than design water flow you will get reduced \ extended pull down due to poor heat transfer.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: pressure drop and chillers

    Quote Originally Posted by Dimitris View Post
    Thanks for the response, but I think I didn't make myself understood. What I meant was if the water flow was higher than normal, would there be any problems in the refrigeration circuit.
    Check this thread:
    http://www.refrigeration-engineer.co...ad.php?t=13199

  6. #6
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: pressure drop and chillers

    Flow rate must be regulated closely, because too low a flow rate reduces chiller efficiency, leading to laminar flow which results in poor heat transfer and short cycling
    The minimum flow rate is typically around 3 ft. per second. However, too high a flow rate leads to vibration, noise and tube erosion. The maximum recommended flow rate is typically around 12 ft. per second.
    Minimum water flow rate is 1.8 GPM per ton of heat exchanger and optimum is 2.4 GPM for a 10*F heat exchanger

  7. #7
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: pressure drop and chillers

    Thanks guys for the posts! I appreciate the time you took to write.

Similar Threads

  1. R22 drop in for a carrier centrif chiller??
    By neil74 in forum Refrigerants
    Replies: 4
    Last Post: 08-01-2008, 02:09 AM
  2. Replies: 2
    Last Post: 21-02-2007, 10:00 PM
  3. Crankcase Pressure Regulator
    By Abe in forum Technical Discussions
    Replies: 32
    Last Post: 10-09-2006, 01:56 PM
  4. Correct drop resistor for LED
    By cooltrain in forum Training
    Replies: 6
    Last Post: 24-12-2004, 11:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •