Thread: pressure drop and chillers
-
27-05-2008, 10:44 PM #1
pressure drop and chillers
When the pressure drop of the water is lower than normal, we usually have a low SST. When the pressure drop is extremely higher than normal, what do you think would happen?
-
28-05-2008, 12:09 AM #2
Re: pressure drop and chillers
If you are talking about the pressure drop across the evaporator then a higher than normal drop means that there is a blockage.
If there is a blockage then the quantity of cooled water is reduced and the chance of a frozen evaporator is increased.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
28-05-2008, 04:16 PM #3
Re: pressure drop and chillers
Thanks for the response, but I think I didn't make myself understood. What I meant was if the water flow was higher than normal, would there be any problems in the refrigeration circuit.
-
29-05-2008, 12:32 AM #4
Re: pressure drop and chillers
With a higher than design water flow you will get reduced \ extended pull down due to poor heat transfer.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-05-2008, 06:19 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: pressure drop and chillers
Check this thread:
http://www.refrigeration-engineer.co...ad.php?t=13199
-
29-05-2008, 07:55 PM #6
Re: pressure drop and chillers
Flow rate must be regulated closely, because too low a flow rate reduces chiller efficiency, leading to laminar flow which results in poor heat transfer and short cycling
The minimum flow rate is typically around 3 ft. per second. However, too high a flow rate leads to vibration, noise and tube erosion. The maximum recommended flow rate is typically around 12 ft. per second.
Minimum water flow rate is 1.8 GPM per ton of heat exchanger and optimum is 2.4 GPM for a 10*F heat exchanger
-
30-05-2008, 08:33 PM #7
Re: pressure drop and chillers
Thanks guys for the posts! I appreciate the time you took to write.
Similar Threads
-
R22 drop in for a carrier centrif chiller??
By neil74 in forum RefrigerantsReplies: 4Last Post: 08-01-2008, 02:09 AM -
Instant water chillers - ammonia recirculation systems
By lraja in forum NH3Replies: 2Last Post: 21-02-2007, 10:00 PM -
Crankcase Pressure Regulator
By Abe in forum Technical DiscussionsReplies: 32Last Post: 10-09-2006, 01:56 PM -
Correct drop resistor for LED
By cooltrain in forum TrainingReplies: 6Last Post: 24-12-2004, 11:09 AM