    Questions about Chiller Design



    Hello everyone,

    Currently I am working on designing a chiller system to provide 30 degree Fahrenheit glycol. Evaporating temperature is about 20 Fahrenheit. The total cooling capacity is 80 tons. I plan to use 9 ten-ton refrigeration systems. One unit is a backup. I would like to use scroll compressors in my design. My questions are:

    1. At 20 degree Fahrenheit evaporating temperature, which refrigerant is better, R404 or R507? Which refrigerant is more efficient and easier to maintain?

    2. I have two options for the condenser: one option is using remote air cooled condenser. The other one is using water cooled condenser and all the 9 chillers share a cooling tower. I wonder which one is the right way to go.

    Please advise if you have any ideas about these questions.

    Many thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Questions about Chiller Design

    I will steer clear of the refrigerant issue, no doubt others will pick it up shortly.

    Condenser?
    You have selected 9 individual units with one in standby at all times should one fail. What will happen if the cooling tower or it's associated water works goes down?

  3. #3
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Questions about Chiller Design

    1. At 20 degree Fahrenheit evaporating temperature, which refrigerant is better, R404 or R507? Which refrigerant is more efficient and easier to maintain?
    Hi . . .

    First what is your condensing design tempreture???
    Knowing the condensing design temp. is critical, once you choose it go for the pressure enthalpy chart and choose the refrigerant with minimum pressure difference between evaporating and condensing tempretures.

    see delta H and go for the greater . . .
    You should do a certain exchange between delta H and minimum evaporating condesnsing pressure . . . do it carefully.

    The greater delta H of evaporator =>less flow.
    The smaller delta p ==> smaller compression ratio.

    Respects and regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  4. #4
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Questions about Chiller Design

    Quote Originally Posted by The Viking View Post
    I will steer clear of the refrigerant issue, no doubt others will pick it up shortly.

    Condenser?
    You have selected 9 individual units with one in standby at all times should one fail. What will happen if the cooling tower or it's associated water works goes down?
    Totaly agree
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  5. #5
    Join Date
    Jun 2005
    Location
    Madison
    Age
    61
    Posts
    32
    Rep Power
    0

    Re: Questions about Chiller Design

    Quote Originally Posted by The Viking View Post
    I will steer clear of the refrigerant issue, no doubt others will pick it up shortly.

    Condenser?
    You have selected 9 individual units with one in standby at all times should one fail. What will happen if the cooling tower or it's associated water works goes down?
    This is a good point. Thanks

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Questions about Chiller Design

    Maybe you can consider to apply evaporative condenser.
    I hear...I forget;I see...I remember;I do...I understand

  7. #7
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Questions about Chiller Design

    AS far as which refrigerant to use for most systems, Honeywell recommends Genetron 404A® or Genetron® AZ-50® (R-507) refrigerants. These products are similar in composition and performance. The key difference is that R-507 is an azeotrope that can be used in flooded evaporators, and has no glide and can be easily recycled or reclaimed without a resulting change in composition.

  8. #8
    Join Date
    May 2006
    Location
    Toronto, Ontario,
    Age
    59
    Posts
    8
    Rep Power
    0

    Re: Questions about Chiller Design

    If you have a choice, always go with water cooled. Just make sure that the cooling towers are always on when you need the chiller, and also ensure your towers have enough capacity.

    Cheers!

  9. #9
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Questions about Chiller Design

    Quote Originally Posted by Vincent Yu View Post

    1. At 20 degree Fahrenheit evaporating temperature, which refrigerant is better, R404 or R507? Which refrigerant is more efficient and easier to maintain?

    2. I have two options for the condenser: one option is using remote air cooled condenser. The other one is using water cooled condenser and all the 9 chillers share a cooling tower. I wonder which one is the right way to go.

    Please advise if you have any ideas about these questions.

    Many thanks

    Item 1. R404 or R507
    - I usually use R507 because the glide is 0.

    Item 2. air cooled or water cooled.

    - I usually use air cooled because the 10 TR condensing unit (ACCU) is readily available in the market. Each compressor with 1 condenser and fan.
    - For lower cost chiller, you may consider buying an aircon ACCU. Just check compressor model if suitable.

  10. #10
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Questions about Chiller Design

    vincent,
    just go for the air cooled condenser.water cooled condenser has high overhead operting expenses compare with air cooled.

Similar Threads

  1. Refrigeration Design Questions
    By UNCrefENGR in forum Fundamentals
    Replies: 18
    Last Post: 06-07-2010, 03:03 AM
  2. Chiller Design
    By munesh in forum Fundamentals
    Replies: 7
    Last Post: 03-06-2008, 09:09 AM
  3. flow through chiller design
    By sucker_dave in forum Technical Discussions
    Replies: 43
    Last Post: 08-09-2006, 06:26 PM
  4. Mini liquid Chiller design
    By Sockit2me in forum Fundamentals
    Replies: 2
    Last Post: 10-02-2006, 06:38 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •