    Plate freezers with stand by system



    We have received an offer from a plate freezer manufacturer which states that
    " To be able to achieve a better freezing
    Only by Having a stand by system - which keeps the plates at Zero Deg during handling time."

    What does this mean?

    What kind of system is expected to be provided by us?



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Plate freezers with stand by system

    I could gather some information on this & it is quite interesting.
    Attached Files Attached Files

  3. #3
    Join Date
    May 2008
    Location
    at the edge of the Arabian Sea!
    Age
    73
    Posts
    36
    Rep Power
    0

    Re: Plate freezers with stand by system

    quite unable to open your pdf files,,,,

    anyway, your question is not clear and infact ought to have been explained by the supplier itself.

    Wht do you intend to convey by stating ''handling time''? Does it mean time to load-unload the freezer or the time spent in defrosting it after each load?

    In the former case , if the freezer has to be loaded the plates should be precooled and if unloaded or defrosted the plates should be allowed to warm up ( by shutting the liquid to it). I do not understand the need for a separate ''stand by system'',,,,perhaps the supplier wants you to opt for a booster system to get lower temp such as -40 C or so.

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Plate freezers with stand by system

    I could see the pdf files.
    What they are recomending is that you run the plate freezers on standby, keeping them at a constant 0c by the use of control valves and solenoids.

    It makes sense to me.
    The plate freezers are kept at 0c untill the product is loaded. Yhis they claim keeps the running costs lower because the temp of the plates and other things are kept on standby at 0c waiting for the product.

    taz.

  5. #5
    Join Date
    May 2008
    Location
    at the edge of the Arabian Sea!
    Age
    73
    Posts
    36
    Rep Power
    0

    Re: Plate freezers with stand by system

    sounds okay to me but in that case you will have to install a separate compressor to keep the plates cool at the time of loading. The actual compressor or booster installed to cool the plates near the critical temp may be employed but it will add to operational cost especially in places where electricity is expensive. Moreover, do you think operators in third world countries are diligent and honest enough to control by valves and by passes etc run the manually controlled machine room precisely as required, especially during night hours ? ,,,,unfortunately I have seen most operators sleeping or drowsing leaving the whole affair in the hands of the inexperienced helper,,,,thereafter I never allowed a bench in the machine room ,,,just a small stool without back

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Plate freezers with stand by system

    Keeping the plates cold would help to increase production rates, however the refrigeration capacity will be greatly reduced with no product freezing so the refrigeration system has to have the same capacity turn down. Otherwise the system may short cycle on small dedicated system. On a central system you might not notice the impact.
    If all else fails, ask for help.


  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Plate freezers with stand by system

    I see a lot of potential service hours on a system like that
    -Cheers-

    Tycho

  8. #8
    Join Date
    Dec 2007
    Location
    Alaska USA
    Age
    71
    Posts
    10
    Rep Power
    0

    Re: Plate freezers with stand by system

    I can't see any benefit from this.
    Plates are getting cold so quick (only few min.) after open liquid valve. Why wasting time and energy to keep them cold when not in use.

    tedre

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  4. Plate freezers
    By smpsmp45 in forum NH3
    Replies: 2
    Last Post: 08-06-2007, 10:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •