    AC charge?



    Will be installing a AC unit next week.The evaporator/air handler is already installed.Unit is capillary system.How do I properly charge the system?Is there a universal chart to go by?I ask this because some of the AC units have confusing charts to go by.Thanks!



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: AC charge?

    If you haven't got any other data, then measuring the subcooling is the most accurate way to charge.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: AC charge?

    Quote Originally Posted by The Viking View Post
    If you haven't got any other data, then measuring the subcooling is the most accurate way to charge.
    It is capillary system and it must be charged by superheat table. One "universal" is Jim wheeler table:


    http://tinyurl.com/56jrzl

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: AC charge?

    Is it just a split unit on running on r22
    Transvestites are men who like to eat, drink, and be Mary.

  5. #5
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: AC charge?

    Thanks for the replies.
    Is it just a split unit on running on r22
    Yes it is a split on R22.

  6. #6
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: AC charge?

    Hmmmm . . .
    try this . . .
    Put the indoor fan speed on high mode ,(first make sure that the dust filters are clean).
    start charging , and measur the tempreture difference between the entering air and the leaving air , once it's about 8 centigrade stop charging.
    for an outdoor tempreture of 26 centigrade the gauge pressure must be about 65 PSIG.

    Not an accurate methode but will work just fine.

    Respects and regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: AC charge?

    [quote=nike123;107439]
    It is capillary system and it must be charged by superheat table
    . [/quote


    This is not the case simply charge system to between 55 to 65 psi ,ie when the suction line sweats back to the compressor , depending on the ambient tempersture but you want to be nearer 65 psi if its a hot day 28c .
    Transvestites are men who like to eat, drink, and be Mary.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: AC charge?

    OK Phil, I'll take the bait...

    With your method, what will happen if:
    -The indoor fan doesn't run at it's rated max capacity?
    -The indoor humidity is below spec.?
    -There are restrictions in the pipework?
    -The indoor ambient temperature is extremely high or low?

    Just some thoughts....


    CRETAN,

    If you give us the manufacturer / model No, then I'm sure we will be able to give you better answers...

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: AC charge?

    Quote Originally Posted by philfridge View Post


    This is not the case simply charge system to between 55 to 65 psi ,ie when the suction line sweats back to the compressor , depending on the ambient tempersture but you want to be nearer 65 psi if its a hot day 28c .

    This is quote from text which link I posted below:



    Capillary/Orifice Metered Systems

    In literally hundreds of visits to problem jobs, I’ve found most air conditioners/heat pumps to be overcharged with refrigerant. Why? Because incorrect charging techniques are too commonly used in the field.
    I remember my first training on charging a residential air conditioner. The technician I worked with said: “Just add refrigerant until the high side is about 250-psig and the low side is about 60.” And that’s how I did it for the first six months of my career as a hvacr service technician.
    Unfortunately, this is the same training many others in our industry received during the building rush of the early ‘70s.
    It’s comforting to know that few still use that method today, but some are even worse! The “Gifted Finger” technique: Adding refrigerant until the suction line turns cold – is one. Another is called the Amprobe Method: you add refrigerant until the compressor reaches rated amps.
    And let’s not forget the Add 35*F approach: this is a little more scientific. You add refrigerant until the saturated condensing temperature is 35*F above the outdoor ambient.

    I know that by now some of you are sitting back and laughing, while others are wondering what’s so funny. I really don’t want to hurt your feelings if you use one of these methods- you certainly aren’t alone or in the minority- but each of these techniques result in an overcharge, and often a GROSS overcharge.
    Back when I used to work as a training manager for a Carrier distributor, I found it strange to find contractors filing claims for 10-lbs. Of refrigerant on systems that only held 6-lbs. However, after several field calls I found many actually WERE putting 10-lbs. Of refrigerant into a6-lbs. systems!
    It’s a common misconception among some technicians [and a few managers] that if you increase refrigerant beyond the specified charge, you increase system capacity. Actually, the opposite is true. Refrigerant added beyond the proper charge reduces capacity. This is because, on capillary or orifice metered equipment, as you add refrigerant you also raise the evaporator temperature.
    The problem with some of these common charging methods, and the reason they shouldn’t be used, is because they fail to address such factors as:
    · Temperature relationships
    · Proper superheat
    · System operating conditions
    · Condenser efficiency

    An overcharge is far more likely to damage the compressor than an undercharge. With capillary and orifice metering devices, excess refrigerant is returned to the crankcase as a constant floodback, reducing capacity, efficiency, and compressor life.
    I only know two ways to properly charge non-TXV [Thermostatic Expansion Valves] systems. Both are simple to use and generally universal in application. They include: the Weight Method and the Superheat Method.
    Weight Method: Weighing charge is simple, quick, and certain. The weight of the factory supplied charge is found on the model/serial number nameplate. If the system has 25-ft. of line [on split systems], the lines aren’t over or undersized, and there’s no field installed liquid line filter dryer, simply weigh the amount shown.

  10. #10
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: AC charge?

    i used the link posted and the chart listed and system works great.thank you everybody for your input!!!!

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: AC charge?

    Quote Originally Posted by cretan View Post
    i used the link posted and the chart listed and system works great.thank you everybody for your input!!!!
    Good to hear that!

  12. #12
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: AC charge?

    Quote Originally Posted by The Viking View Post
    OK Phil, I'll take the bait...

    With your method, what will happen if:
    -The indoor fan doesn't run at it's rated max capacity?
    -The indoor humidity is below spec.?
    -There are restrictions in the pipework?
    -The indoor ambient temperature is extremely high or low?
    I have the gifted finger
    Transvestites are men who like to eat, drink, and be Mary.

  13. #13
    Join Date
    Jun 2008
    Location
    United States
    Age
    72
    Posts
    11
    Rep Power
    0

    Re: AC charge?

    Quote Originally Posted by cretan View Post
    i used the link posted and the chart listed and system works great.thank you everybody for your input!!!!
    I've been through jim Wheeler's charging discussion numerous times as refresher course, but what "chart" is "listed" or do you just mean the appropriate pressure temp chart for the refrigerant involved?

    I was going to post the one's I've been using but I don't seem to have 15 posts in, seems like I must have hundreds, but maybe just because it has been a problem week that lead me to seek out this board.

    Soon as I am able I will post the links.

    Brian

  14. #14
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: AC charge?

    the unit I was working on was originally a water cooled unit.i replaced it with an air cooled condensor.i did not have a charging chart to go by.the chart on the link seemed to work fine.if you have other charts I would be interested.

Similar Threads

  1. low charge or cap tube blockage?
    By NC joe in forum Commercial
    Replies: 8
    Last Post: 02-09-2009, 02:53 PM
  2. To charge or not to charge?
    By Fire and Ice in forum Old Refrigeration Photos
    Replies: 12
    Last Post: 20-01-2008, 08:11 PM
  3. Help please. How to charge a unit
    By God55 in forum Air Conditioning
    Replies: 18
    Last Post: 23-03-2007, 10:07 AM
  4. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Replies: 4
    Last Post: 01-12-2006, 07:40 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •