    Red face Mitsubishi PU-3VJC



    I have a problem with a mitsubishi PU-3VJC unit... A new compressor was installed a couple of months back, and now the unit runs fine for about two cycles after getting down to temperature and starting up again.

    The third time the unit starts up, the contactor pulls in and only the fans come on with no compressor as it has gone out on its thermal overload. The fault code on the controller shows problem with outdoor unit.

    I'm thinking there is a blockage in the capillary. Could someone please validate this for me if they think it is the same problem... or anything else...? Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi PU-3VJC

    We need some more information to answer this one I think.

    Is the compressor hot to the touch ?

    What are the operating pressures/temperatures?

    Overheating could be due to a gas shortage, is the charge correct?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2006
    Location
    England
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi PU-3VJC

    Yes, the compressor is really hot. each time it starts up it gets hotter. i recorded the top of the compressor at around 140 degrees when it cut out the second time, this is why i think its cutting out on its thermal overload, and not starting up the third time.
    And there is a correct charge of gas. each time the pressures rise a little higher... its an R22 system, running at around 35psi on the suction and before cut out on the second run at around 45psi.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi PU-3VJC

    Quote Originally Posted by C_Henderson View Post
    And there is a correct charge of gas. each time the pressures rise a little higher... its an R22 system, running at around 35psi on the suction and before cut out on the second run at around 45psi.
    Indications are a shortage of gas with that pressure, Mitsi A/C is normally around 50+psig.
    You are not getting any compressor cooling from the returning gas.

    What is the superheat ?
    Also a discharge pressure would be helpful if that model has a pressure test point.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Mitsubishi PU-3VJC

    Hi C henderson

    This may be a possibility if its a heatpump, there may be a slight chance that the reversing valve may be slightly passing gas back to the suction but without a head guage on you want know, dont let the low suction pressure fool you that the above is not happening we got caught out twice with this happening and the compressors overheated.

    Regards
    LRAC

  6. #6
    Join Date
    Jul 2006
    Location
    England
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi PU-3VJC

    the unit isnt a heat pump, so theres no worries with the reversing valve...

    im pretty sure the gas charge is fine as i put in the stated amount plus a little more as i thought the pressures were too low...

    im thinkin theres a restriction or small bloackage somewhere, ei the capillary?

  7. #7
    rbartlett's Avatar
    rbartlett Guest

    Re: Mitsubishi PU-3VJC

    Quote Originally Posted by LRAC View Post
    Hi C henderson

    This may be a possibility if its a heatpump, there may be a slight chance that the reversing valve may be slightly passing gas back to the suction but without a head guage on you want know, dont let the low suction pressure fool you that the above is not happening we got caught out twice with this happening and the compressors overheated.

    Regards
    LRAC

    I'm willing to bite on this one.

    The refrigerant charge is correct by weight

    so a high pressure of -say- 220 psig is leaking into a low pressure of -say- 50 psig and the result is a lower pressure of 35psig.but he shouldn't be fooled by this...

    please explain the dynamics of your reasoning ...

    cheers

    richard

  8. #8
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Mitsubishi PU-3VJC

    Hi

    me tthinks the thing isn't condensing properly, but without head pressure, liquid line pressure and liquid temperature it is hard to say

    But if I had to guess I would say it is a condensing problem, fan, card or control probe problem

    Kind Regards Andy

    PS why will engineers not fit shrider connection on the head side when changing compressors, seens to be a very common problem
    If you can't fix it leave it that no one else will:rolleyes:

  9. #9
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Mitsubishi PU-3VJC

    Quote Originally Posted by rbartlett View Post
    I'm willing to bite on this one.

    The refrigerant charge is correct by weight

    so a high pressure of -say- 220 psig is leaking into a low pressure of -say- 50 psig and the result is a lower pressure of 35psig.but he shouldn't be fooled by this...

    please explain the dynamics of your reasoning ...

    cheers

    richard
    Hi all
    who said anything about a head preasure reading, no indication was given on any readings,if a reversing valve is stuck then no heat is being absorbed by the the indoor unit as the refrigerent is not being processed .i.e no duty in the condenser and a possibility of a complete short cycle of the circuit. The compressor would be completly cycling its own charge with the indication of the above happening.

    No head pressure and no suction pressure if left to run long enough you get overheating of the compressor.

    Ok i know it sounds completly wrong but here's the crunch, the refrigerent charge may have already been sitting in the evap and pipe runs and with the valve stuck the existing refrigerent will not move from its resting area if a valve is passing causing low pressures. All i can do is report on equipment history our engineers find and the faults they report.

    Anything is possible if you think about it.

    Regards
    LRAC

  10. #10
    rbartlett's Avatar
    rbartlett Guest

    Re: Mitsubishi PU-3VJC

    Quote Originally Posted by LRAC View Post
    Hi all
    who said anything about a head preasure reading, no indication was given on any readings,if a reversing valve is stuck then no heat is being absorbed by the the indoor unit as the refrigerent is not being processed .i.e no duty in the condenser and a possibility of a complete short cycle of the circuit. The compressor would be completly cycling its own charge with the indication of the above happening.
    C_Henderson-
    And there is a correct charge of gas. each time the pressures rise a little higher... its an R22 system, running at around 35psi on the suction and before cut out on the second run at around 45psi.

    No head pressure and no suction pressure if left to run long enough you get overheating of the compressor.
    This doesn't mean anything. no suction pressure or head pressure indicates a total loss of charge that is all. A zero differential may indicate a rv fault.

    Ok i know it sounds completly wrong but here's the crunch, the refrigerent charge may have already been sitting in the evap and pipe runs and with the valve stuck the existing refrigerent will not move from its resting area if a valve is passing causing low pressures. All i can do is report on equipment history our engineers find and the faults they report.
    It only sounds completely wrong because it IS completely wrong.!! A bypass situation can only lead to a higher than normal operating suction pressure not a lower one.The 'refrigerant in the pipes' is nonsense as far as I'm concerned in this application.

    Please scan some of your guy's reports as I'd love to read them

    Anything is possible if you think about it.
    Thinking something is possible doesn't actually make it so..

    Cheers

    richard

  11. #11
    Join Date
    Jul 2006
    Location
    Australia
    Age
    52
    Posts
    28
    Rep Power
    0

    Re: Mitsubishi PU-3VJC

    i'm noone but simple question ? when you replaced compressor did you check system with acid kit?
    Did you installed suction filter drayer?

  12. #12
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Mitsubishi PU-3VJC

    I think you need to go back to the basics.
    Why did the first comp fail?
    Was the second comp fitted correctly?
    Was a correct dehumidification and gas charge take place?
    Has the second comp been showing signs of failure from the start or is it getting progressivley worse?
    Comp running amps, head preasure and back pressure all need logging so correct opperation can be determined.
    If there is any chance that the cond fan is at fault, by pass the control and run it perminatly to rule out.
    You must garentee that no air is in the system.

    Good luck cheers taz.

  13. #13
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Mitsubishi PU-3VJC

    what indoor unit is it?

  14. #14
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Mitsubishi PU-3VJC

    just a thought OFN still in the system after 1st comp change?
    Paul


    "KEEP IT COOL"

  15. #15
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Mitsubishi PU-3VJC

    Quote Originally Posted by MRcoolingMAGIC View Post
    it is from 2006 ...probaly they changed the system by now
    guess we will never know,i love feedback
    Paul


    "KEEP IT COOL"