    A/c Water Chiller



    Hi,
    im new to water chiller for aircon application,and i have some question,
    a.on a close system which i assume since there is no expansion tank when we fill it up with water do we
    need to add chemical or neutralizer?
    b.what is the avarage flow rate of water?
    c.if the system is running ,do we need to add water in the future?
    please,help is greatly appreciated.



  2. #2
    Join Date
    Apr 2008
    Location
    Dubai, UAE
    Posts
    16
    Rep Power
    0

    Re: A/c Water Chiller

    Hi Abet,

    Welcome to RE!

    a.on a close system which i assume since there is no expansion tank when we fill it up with water do we
    need to add chemical or neutralizer?
    - it depends on the quality of water you are going to chill: TDS, hardness......etc.

    b.what is the avarage flow rate of water?
    -What type of evaporator you are going to use; S&T, PHE....?
    c.if the system is running ,do we need to add water in the future?
    - YES. this depends on the type of system you designed. Mostly, they install buffer tanks with level controls that if the level is below limit, it automatically refills the media

  3. #3
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    16

    Question Re: A/c Water Chiller

    Thanks alphi
    the evaporator is a shell and tube type.water coil unit is on the AHU room.what is the average water pressure?
    Last edited by abet_meneses; 26-05-2008 at 03:30 PM.

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: A/c Water Chiller

    Quote Originally Posted by abet_meneses View Post
    Hi,
    im new to water chiller for aircon application,and i have some question,
    a.on a close system which i assume since there is no expansion tank when we fill it up with water do we
    need to add chemical or neutralizer?
    b.what is the avarage flow rate of water?
    c.if the system is running ,do we need to add water in the future?
    please,help is greatly appreciated.
    A. (a) There must be an expansion vessel, how would the system otherwise cope with expansion/retraction of the water as it changes temperature?
    A. (b) Chemicals... Depending on the working temperature of the chiller, Glycol will be required (also remember to check the saturated temp of the refrigerant in the evaporator). Inhibitor to prevent rust and slime build-up is always a good idea.

    B. Depends on the duty of your chiller, see specification by manufacturer.

    C. Shouldn't but probably will have to at some point.


    Pressure? 1 bar = 10 metres of water column. Just ensure that your installation at all points is under positive pressure. (Remember, if the pumpset is at the highest point of the system, the pressure going in to the pump(s) will be lower than the flow pressure but still needs to be positive)

  5. #5
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    16

    Re: A/c Water Chiller

    Viking,
    thanks for value info.will visit your website

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Exclamation Re: A/c Water Chiller

    watch your systems handbook before you put in glycol. not all glycol is safe.

    you can damage the pumps or heatexchanger.
    see at whitch temp it will work, and calculate the amound of glycol.
    also glycol will help to get better working temps

    read the installation manual first,

    Cya, Ice

  7. #7
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    16

    Re: A/c Water Chiller

    ice cube,
    many thanks ,since ours is a tropical country ,we do not use glycol on water chiller a/c application.

Similar Threads

  1. water chiller question
    By chillman in forum Technical Speculations
    Replies: 2
    Last Post: 12-03-2008, 10:21 PM
  2. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  3. Water chiller help
    By ultralo1 in forum Trouble Shooting
    Replies: 6
    Last Post: 12-05-2007, 11:52 AM
  4. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 07:14 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •