25-05-2008, 05:27 PM #1
Vacuum Pump CFM
Hello,
i like to know how to calculate a vacuum pump capacity cfm, use for vacuum big chiller like 1000 Ton,
Thanks,
31-08-2008, 03:52 AM #2
Re: Vacuum Pump CFM
Hi! Based on my experienced dealing with AC Chiller Units and higher tonnages. I don't have calculation as long as within the range of safe where no moisture present. You need to isolate the unit each part by part. Use the dual stage vacuum pump. Add refrigerant then purging.
31-08-2008, 10:49 AM #3
Re: Vacuum Pump CFM
First of all;
PLEASE DO NOT PURGE SYSTEMS WITH REFRIGERANT, the polar bears are already suffering and dying.
Use nitrogen instead.
When it comes to vacuum pumps;
The CFM itself is less important, a small pump correctly attached to the system will pull a quicker vacuum than a larger pump connected through a manifold.
Instead of using manifold and hoses, use CU-pipes and flares, also, utilise "valved" service ports and not schraeders (if you have to, use a core removal tool). This will speed up your work more than a larger pump will do.
Good luck.
25-10-2008, 03:13 PM #4
Re: Vacuum Pump CFM
why not try the tripple evacuation method , using a torr gauge when at desered vac add ofn up to atmosferic pressure then do it twice more.
25-10-2008, 07:33 PM #5
Re: Vacuum Pump CFM
Sedy, i use the same technique but only twice.
26-10-2008, 03:52 PM #6
26-10-2008, 11:22 PM #7
Re: Vacuum Pump CFM
so I take it that nowboady has used the tripple vac system ? well it is faster
27-10-2008, 12:06 AM #8
27-10-2008, 12:26 AM #9
Re: Vacuum Pump CFM
Can someone explain the procedures of triple vacuuming? Thanx
Smart remarks come from smart people.
27-10-2008, 01:27 PM #10
Re: Vacuum Pump CFM
Triple evacuation
1. Recover system charge.
2. Replace filter drier and pressure test.
3. Evacuate to first stage pressure. (e.g. for 20C - 31mbar)
4. Break the vacuum with OXYGEN FREE dry nitrogen to ¼ barg and hold for 5 min.
5. Evacuate to second stage pressure. (e.g. for 20C - 25mbar)
6. Break the vacuum with OXYGEN FREE dry nitrogen to ¼ barg and hold for 5 min.
7. Evacuate to third stage pressure. (e.g. for 20C - 9 to 11mbar)
The plant should now be sufficiently dehydrated and suitable for recharging.Tony
27-10-2008, 03:10 PM #11
Re: Vacuum Pump CFM
The volume (CFM) ratings on vacuum pumps are with the intake wide open. Volume drops considerably when the pump is pulling through gauges, hoses and fittings.
Try breathing through a straw and you get the picture. How much air you get depends upon the diameter of the straw.
Similarly, when evacuating, the size of the hoses and fittings is more important than the volume rating of the pump.
27-10-2008, 03:20 PM #12
Re: Vacuum Pump CFM
It also helps if you pull from multiple locations in the system. Pulling a vacuum from a single point is similar to using hoses with high flow restrictions.
I like the concept of using copper tubing also, instead of charging hoses.If all else fails, ask for help.
Compressor ID for DIY vacuum pump
By mikemac in forum DomesticReplies: 22Last Post: 05-05-2010, 10:39 AM -
Vacuum pump CFM's?
By mooka in forum Air ConditioningReplies: 20Last Post: 12-04-2008, 03:15 PM -
inverters pulling vacuum
By bangoman in forum Air ConditioningReplies: 2Last Post: 05-02-2008, 10:12 PM -
Vacuum pump cleaning and POE!
By The MG Pony in forum FundamentalsReplies: 8Last Post: 31-03-2007, 06:06 PM -
car engine oil in compressor used as vacuum pump for laser
By star882 in forum Technical SpeculationsReplies: 3Last Post: 05-11-2005, 03:09 PM