    Vacuum Pump CFM



    Hello,
    i like to know how to calculate a vacuum pump capacity cfm, use for vacuum big chiller like 1000 Ton,

    Thanks,



  2. #2
    Join Date
    Aug 2006
    Location
    Philippines
    Age
    52
    Posts
    7
    Rep Power
    0

    Re: Vacuum Pump CFM

    Hi! Based on my experienced dealing with AC Chiller Units and higher tonnages. I don't have calculation as long as within the range of safe where no moisture present. You need to isolate the unit each part by part. Use the dual stage vacuum pump. Add refrigerant then purging.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Vacuum Pump CFM

    First of all;
    PLEASE DO NOT PURGE SYSTEMS WITH REFRIGERANT, the polar bears are already suffering and dying.
    Use nitrogen instead.

    When it comes to vacuum pumps;
    The CFM itself is less important, a small pump correctly attached to the system will pull a quicker vacuum than a larger pump connected through a manifold.

    Instead of using manifold and hoses, use CU-pipes and flares, also, utilise "valved" service ports and not schraeders (if you have to, use a core removal tool). This will speed up your work more than a larger pump will do.

    Good luck.

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Vacuum Pump CFM

    why not try the tripple evacuation method , using a torr gauge when at desered vac add ofn up to atmosferic pressure then do it twice more.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Vacuum Pump CFM

    Sedy, i use the same technique but only twice.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Vacuum Pump CFM

    Quote Originally Posted by w.l.ong View Post
    Hello,
    i like to know how to calculate a vacuum pump capacity cfm, use for vacuum big chiller like 1000 Ton,

    Thanks,
    This post is slightly old now.
    But just in case it's still relevant,
    Yellow jacket reccomend that when a system is 60ton and above,
    11CFM is required. (and a lot of patience!)
    Grizzly

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Vacuum Pump CFM

    so I take it that nowboady has used the tripple vac system ? well it is faster

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Vacuum Pump CFM

    Quote Originally Posted by sedgy View Post
    so I take it that nowboady has used the tripple vac system ? well it is faster
    Why do you take it that way.

    Most people know of the triple evac and can/do use when required.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Vacuum Pump CFM

    Can someone explain the procedures of triple vacuuming? Thanx
    Smart remarks come from smart people.

  10. #10
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Vacuum Pump CFM

    Triple evacuation

    1. Recover system charge.

    2. Replace filter drier and pressure test.

    3. Evacuate to first stage pressure. (e.g. for 20C - 31mbar)

    4. Break the vacuum with OXYGEN FREE dry nitrogen to ¼ barg and hold for 5 min.

    5. Evacuate to second stage pressure. (e.g. for 20C - 25mbar)

    6. Break the vacuum with OXYGEN FREE dry nitrogen to ¼ barg and hold for 5 min.

    7. Evacuate to third stage pressure. (e.g. for 20C - 9 to 11mbar)

    The plant should now be sufficiently dehydrated and suitable for recharging.
    Tony

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Vacuum Pump CFM

    The volume (CFM) ratings on vacuum pumps are with the intake wide open. Volume drops considerably when the pump is pulling through gauges, hoses and fittings.

    Try breathing through a straw and you get the picture. How much air you get depends upon the diameter of the straw.

    Similarly, when evacuating, the size of the hoses and fittings is more important than the volume rating of the pump.

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Vacuum Pump CFM

    It also helps if you pull from multiple locations in the system. Pulling a vacuum from a single point is similar to using hoses with high flow restrictions.

    I like the concept of using copper tubing also, instead of charging hoses.
    If all else fails, ask for help.


Similar Threads

  1. Compressor ID for DIY vacuum pump
    By mikemac in forum Domestic
    Replies: 22
    Last Post: 05-05-2010, 10:39 AM
  2. Vacuum pump CFM's?
    By mooka in forum Air Conditioning
    Replies: 20
    Last Post: 12-04-2008, 03:15 PM
  3. inverters pulling vacuum
    By bangoman in forum Air Conditioning
    Replies: 2
    Last Post: 05-02-2008, 10:12 PM
  4. Vacuum pump cleaning and POE!
    By The MG Pony in forum Fundamentals
    Replies: 8
    Last Post: 31-03-2007, 06:06 PM
  5. car engine oil in compressor used as vacuum pump for laser
    By star882 in forum Technical Speculations
    Replies: 3
    Last Post: 05-11-2005, 03:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •