Results 1 to 12 of 12
Thread: Vacuum Pump CFM
    Jun 2005
    Malaysia
    28
    Vacuum Pump CFM
    Hello,
    i like to know how to calculate a vacuum pump capacity cfm, use for vacuum big chiller like 1000 Ton,
    Thanks,
    Philippines
    52
    7
    Re: Vacuum Pump CFM
    Hi! Based on my experienced dealing with AC Chiller Units and higher tonnages. I don't have calculation as long as within the range of safe where no moisture present. You need to isolate the unit each part by part. Use the dual stage vacuum pump. Add refrigerant then purging.
    Feb 2007
    2,473
    Re: Vacuum Pump CFM
    First of all;
    PLEASE DO NOT PURGE SYSTEMS WITH REFRIGERANT, the polar bears are already suffering and dying.
    Use nitrogen instead.
    When it comes to vacuum pumps;
    The CFM itself is less important, a small pump correctly attached to the system will pull a quicker vacuum than a larger pump connected through a manifold.
    Instead of using manifold and hoses, use CU-pipes and flares, also, utilise "valved" service ports and not schraeders (if you have to, use a core removal tool). This will speed up your work more than a larger pump will do.
    Good luck.
    Oct 2008
    mallorca, spain,
    75
    768
    Re: Vacuum Pump CFM
    why not try the tripple evacuation method , using a torr gauge when at desered vac add ofn up to atmosferic pressure then do it twice more.
    Oct 2003
    5,630
    Re: Vacuum Pump CFM
    Sedy, i use the same technique but only twice.
    4,697
    Re: Vacuum Pump CFM
    Quote Originally Posted by w.l.ong View Post
    Hello,
    Thanks,
    This post is slightly old now.
    But just in case it's still relevant,
    Yellow jacket reccomend that when a system is 60ton and above,
    11CFM is required. (and a lot of patience!)
    Oct 2008
    mallorca, spain,
    75
    768
    Re: Vacuum Pump CFM
    so I take it that nowboady has used the tripple vac system ? well it is faster
    11,025
    Re: Vacuum Pump CFM
    Quote Originally Posted by sedgy View Post
    Why do you take it that way.
    Most people know of the triple evac and can/do use when required.
    Aug 2008
    44
    Re: Vacuum Pump CFM
    Can someone explain the procedures of triple vacuuming? Thanx
    Smart remarks come from smart people.
    Feb 2001
    Doncaster, England
    199
    Re: Vacuum Pump CFM
    Triple evacuation
    1. Recover system charge.
    2. Replace filter drier and pressure test.
    3. Evacuate to first stage pressure. (e.g. for 20C - 31mbar)
    4. Break the vacuum with OXYGEN FREE dry nitrogen to ¼ barg and hold for 5 min.
    5. Evacuate to second stage pressure. (e.g. for 20C - 25mbar)
    6. Break the vacuum with OXYGEN FREE dry nitrogen to ¼ barg and hold for 5 min.
    7. Evacuate to third stage pressure. (e.g. for 20C - 9 to 11mbar)
    The plant should now be sufficiently dehydrated and suitable for recharging.
    Tony
    Apr 2001
    79
    5,071
    35
    Re: Vacuum Pump CFM
    The volume (CFM) ratings on vacuum pumps are with the intake wide open. Volume drops considerably when the pump is pulling through gauges, hoses and fittings.
    Try breathing through a straw and you get the picture. How much air you get depends upon the diameter of the straw.
    Similarly, when evacuating, the size of the hoses and fittings is more important than the volume rating of the pump.
    Aug 2005
    5,302
    Re: Vacuum Pump CFM
    It also helps if you pull from multiple locations in the system. Pulling a vacuum from a single point is similar to using hoses with high flow restrictions.
    I like the concept of using copper tubing also, instead of charging hoses.
  1. Compressor ID for DIY vacuum pump
    By mikemac in forum Domestic
    Last Post: 05-05-2010, 10:39 AM
  2. Vacuum pump CFM's?
    By mooka in forum Air Conditioning
    Last Post: 12-04-2008, 03:15 PM
  3. inverters pulling vacuum
    By bangoman in forum Air Conditioning
    Last Post: 05-02-2008, 09:12 PM
  4. Vacuum pump cleaning and POE!
    By The MG Pony in forum Fundamentals
    Last Post: 31-03-2007, 06:06 PM
  5. car engine oil in compressor used as vacuum pump for laser
    By star882 in forum Technical Speculations
    Last Post: 05-11-2005, 02:09 PM