    Post Propane compressor suction drum level issues



    Please advice,

    We have a problem similar to that as described by Achmed; Propane compressor where the suction drum builds up a propane liquid level which could lead to a compressor trip.

    Although we don't have any issues during spring/winter months we have issues when the ambient temperature increases above the 35°C (during the Southern Hemisphere summer months the ambient temperature can reach up to 50°C)

    Any suggestions?

    Thanks



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Propane compressor suction drum level issues

    Welcome to the RE forums.

    The most likely possibility is that the liquid is accumulating in the suction knock-out drum from periodic liquid carryover from the evaporators.

    This could be caused by process upsets where the compressors might load up quickly and cause the liquid to boil violently in the evaporator. this could cause the liquid carryover.

    Another case might be the process load increases quickly for some reason, which could cause the above to happen also.

    In either case, the liquid carryover may accumulate in the knock-out drum until the liquid level trips the high level shut down float switch.
    Last edited by US Iceman; 25-05-2008 at 01:49 AM. Reason: spelling
    If all else fails, ask for help.


  3. #3
    inuendo's Avatar
    inuendo Guest

    Re: Propane compressor suction drum level issues

    Hi US Iceman

    Thanks for the response, unfortunately none of the suggested upset conditions occur. The increase in level in the suction drum level will happen only during extreme hot ambient temperatures, the level increases over a period of 10 hrs from 2% to 15%. When the temperature goes down late in the afternoon usually around 17.00hrs the level slowly decreases.
    I'm thinking more in SG changes but I'm not sure how to explain this phenomenon.
    Cheers

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Propane compressor suction drum level issues

    Hi Inu.
    sounds like expansion control devises are overfeeding at high ambient. More condensing required during heat of the day
    Magoo

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Propane compressor suction drum level issues

    Hi again Inuendo. To explain further expansion valve are rated on press differential across valve, increase the hih side and the flow rate increase to evaporator, the trick is to install an accumulator to trap over feed from entering compressor. A rule of thumb is to be able hold 80% of system charge and a safety margin.
    Magoo

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Propane compressor suction drum level issues

    Quote Originally Posted by inuendo
    I'm thinking more in SG changes but I'm not sure how to explain this phenomenon.
    If this is indeed a suction knock-out drum then specific gravity shouldn't have anything to do with it. The pressure in the vessel should be relatively constant so the liquid density on the suction side should not be affected.

    Barring any process upsets then I would have to say your problem is related to some control valve(s) overfeeding during this 10 hour period. It would seem from your descriptions that the overfeeding occurs as the pressure differential increases due to high discharge pressures (i.e., related to an increase in warm ambient temperatures).

    Without seeing any P&ID's I can only guess what the general issue might be. However, somewhere in your system it would appear there is a control that is being fed by high-pressure liquid propane. As the pressure differential increases (suction is relatively fixed, while the discharge pressure continues to increase through the day) the flow capacity of a control valve increases. If the controller does not force the valve to throttle down, it will simply flow to much.

    The fact that the liquid level goes down in the cooler periods would tend to reinforce this as this discharge pressure should be decreasing during this time. I'm assuming you are using air-cooled exchangers.

    By any chance does the knock-out drum have a liquid feed valve upstream to provide desuperheating of the suction gas before the gas enters the vessel?
    If all else fails, ask for help.


  7. #7
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Propane compressor suction drum level issues

    I have to go along the lines with US Iceman. The ris something basically wrong with the design of the evaporator if you are getting liquid over into the suction drum on a regular basis.

    Can you describe the evaporator and tell us how much vertical disengaging space you have. It would really help to see the design drawings and data sheets on the evaporator.

    A section drum (accumulator) should be dry except in the case of a process upset.

    Who designed the evaporator and suction drum? If it was one of the process design companies, they generally do not understand the requirements of a refrigeraiton evaporator and suction drum. I have yet to see a non-refrigeration company properly design an evaporator and suction drum. They will always be short on disengaging space and run the separation velocities too high which will lead to a continual liquid carry over from the evaporator which will over fill the suction drum.

    I like to design a suction drum with a "boil-out coil" to insure that there is a reasonable way to disapate any liquid carried to the suction drum.

    If you can get some drawings and data sheets to me or US Iceman, we can look them over.

    Ken

  8. #8
    inuendo's Avatar
    inuendo Guest

    Re: Propane compressor suction drum level issues

    Thank you all for responding to my question, I will get you the details as requested. When I have returned back to work I will gather this info.

    Kind regards

  9. #9
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    66
    Posts
    78
    Rep Power
    21

    Re: Propane compressor suction drum level issues

    question 1
    what is temperature of suction gas before suction drum
    is suction drum colder then the gas condensation will occur.
    assuming rest of installation is oke
    we always assume suction is warmer as the drum
    but it does not have to be like in your case
    computer shooter
    paul deelen
    +31653300739

Similar Threads

  1. Replies: 23
    Last Post: 06-06-2008, 02:27 PM
  2. propane compressor suction drum
    By Ahmed_LNG in forum Technical Discussions
    Replies: 2
    Last Post: 03-01-2006, 10:31 PM
  3. propane compressor suction drum
    By Ahmed_LNG in forum Refrigerants
    Replies: 7
    Last Post: 01-01-2006, 08:01 AM
  4. propane compressor suction drum
    By Ahmed_LNG in forum Trouble Shooting
    Replies: 0
    Last Post: 30-12-2005, 06:08 AM
  5. propane compressor suction drum
    By Ahmed_LNG in forum Industrial Compressors
    Replies: 0
    Last Post: 30-12-2005, 06:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •