    Cap Tube on prep table keeps plugging up



    Prep table with 134a. Replaced evap in prep table as well as the pencil drier to an emerson cap-t style. on a return call I found that the cap tube had a restriction in it, so I changed the cap tube and drier and recharged, pressures were 20 psi and 175 psi. Then 3 days later got called back again and found suction 1 psi and hi side at 135 psi, now I believe the cap tube has restriction again. it is most likely the original compressor and I was told to change the old poe oil to new poe. Any ideas or would you agree with changing the oil



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Cap Tube on prep table keeps plugging up

    How good vacuum did you get the unit down to after each time the circuit were opened?

    Changing the oil is a good move, but only if you make sure the whole system is flushed with OFN and vacced properly.

  3. #3
    Join Date
    May 2008
    Location
    Canada
    Posts
    5
    Rep Power
    0

    Re: Cap Tube on prep table keeps plugging up

    decided to go ahead with the oil change. during that i managed to also remove about a table spoon of water from the suction line wich was clearly the issue. as well through another cap tube and drier on.
    thanks

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Cap Tube on prep table keeps plugging up

    Quote Originally Posted by toes View Post
    decided to go ahead with the oil change. during that i managed to also remove about a table spoon of water from the suction line wich was clearly the issue. as well through another cap tube and drier on.
    thanks
    That mean that you in first service did not made proper evacuation. Now, you still have some contaminants (acids) in the oil because you did not make flushing. Check oil acidity and fit burn-out filter before and after compressor if needed, and change them after some time (check pressure drop across them and after making check that oil acidity is acceptable), or you could end up soon with new service call for compressor burnout.

Similar Threads

  1. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Replies: 4
    Last Post: 15-11-2007, 07:03 AM
  2. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Replies: 15
    Last Post: 03-04-2007, 08:25 PM
  3. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 07:57 AM
  4. Information on frost top prep table
    By kengineering in forum Commercial
    Replies: 15
    Last Post: 08-02-2006, 10:58 AM
  5. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 08:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •