    Water Chiller High Water Flow



    Hi we all know what happens if we have insufficient water flow through an evaporator, the suction pressure will drop, the evaporator can freeze and liquid refrigerant can smash up the compressor.

    What happens if we have too much water flow through an evaporator.
    Obviously insufficient heat will be removed from the water and our suction and discharge pressures will go up

    But what else

    Regards Assad



  2. #2
    Join Date
    May 2006
    Location
    Toronto, Ontario,
    Age
    59
    Posts
    8
    Rep Power
    0

    Re: Water Chiller High Water Flow

    With low flow I have also found a problem with oil. The oil stays in the evap because of low velocity and the unit may trip on oil fail b4 low pressure. The tech may then add more oil to a point where the unit will have too much and oil slugging will occur. This is more likely the cause of a smashed compressor rather than liquid refrigerant.

    The amount of heat removed in total BTU's or KW will remain the same regardless of flow speed (up to a limit). If your unit has an excessive amount of flow, the unit will still function as long as the total load has not changed. What will happen is that your evap will wear prematurely and one of the tubes will leak and cause refrigerant loss and then a wet system.

  3. #3
    Join Date
    May 2008
    Location
    UK
    Age
    53
    Posts
    8
    Rep Power
    0

    Re: Water Chiller High Water Flow

    The reason for the question is we have a site which over the last few years has suffered numerious compressor failures (Smash Ups) up to recently it has belived it was poor water flow through the evapourator.
    Now they have found it is too much water flow through the evapourator. I don't believe that too much water flow through the evapourator would cause compressor failures and this is the debate we are having in the office at pressent.
    Regards Assad

  4. #4
    teacher's Avatar
    teacher Guest

    Re: Water Chiller High Water Flow

    Too much waterflow can make that the evaporationpressure or the sunctionpressure gets too high for the compressor.
    Rob

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Water Chiller High Water Flow

    Why not check the manual, there is a minimum and maximum water flow.
    just follow it and you are safe.



    Chemi

  6. #6
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    18

    Re: Water Chiller High Water Flow

    What about compressors starting too many times per hour?

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Water Chiller High Water Flow

    If water flow is too high, the chiller usually will not reach it's setpoint, unless there is also a hydraulic issue in the building and the machine left running with lower loads then acceptable!

    What machine are we talking about?

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Water Chiller High Water Flow

    Quote Originally Posted by Lowrider View Post
    If water flow is too high, the chiller usually will not reach it's setpoint, unless there is also a hydraulic issue in the building and the machine left running with lower loads then acceptable!
    Could you describe this, because I don't see why chiller will not reach it's setpoint.

  9. #9
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Water Chiller High Water Flow

    Quote Originally Posted by nike123 View Post
    Could you describe this, because I don't see why chiller will not reach it's setpoint.
    Say you have a chiller of 1MW and building load is more than the capacity of the chiller. If flow through is constant, which it should be, the chiller will not reach it's setpoint because no mather what happens, if the flow is say double that of what it should be, the chiller if designed for 6K will only do 3K. If the load from the building stay's higher than the chiller capacity the chiller will keep running and never reaches it's setpoint.

    On the other hand, if building load is less the chiller minimal capacity, having the higher flow will keep the chiller on longer! which in this case is a good thing!

    It's all down to Q=m*c*dT

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Water Chiller High Water Flow

    Quote Originally Posted by Lowrider View Post

    On the other hand, if building load is less the chiller minimal capacity, having the higher flow will keep the chiller on longer! which in this case is a good thing!

    It's all down to Q=m*c*dT
    OK, my question was referring at this quoted situation!

  11. #11
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Water Chiller High Water Flow

    What situation? We only know he has a problem, not the type and size of the machine, hydraulic lay out, flow's, etc.

    Generaly taken a chiller with too much flow will not reach it's setpoint untill the load drops!

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by Lowrider View Post
    What situation? We only know he has a problem, not the type and size of the machine, hydraulic lay out, flow's, etc.

    Generaly taken a chiller with too much flow will not reach it's setpoint untill the load drops!
    Of course that chiller would not reach his set point when building load is higher then chiller capacity.
    I questioned that chiller will not reach set point when his capacity is higher then load, but flow thru evaporator is higher then nominal.
    At least, that is how I understood your post #7!

    I am with chillin here:
    The amount of heat removed in total BTU's or KW will remain the same regardless of flow speed (up to a limit). If your unit has an excessive amount of flow, the unit will still function as long as the total load has not changed.
    I have capacity correction factors for chillers that I service (Galletti):
    dT 3K =0,975
    dT 4K =0,990
    dT 5K=1
    dT 6K=1,015
    dT 7K=1,030
    dT 8K=1,040


    Flow variation with change from nominal dT of 5K to 3K is 63% more flow then nominal.
    That mean, 63% more flow wil make drop in capacity of 2,5%.
    I don't see at what you base your statemant:
    If water flow is too high, the chiller usually will not reach it's setpoint, unless there is also a hydraulic issue in the building and the machine left running with lower loads then acceptable!
    Last edited by nike123; 21-05-2008 at 12:04 AM. Reason: Adding some clarification

  13. #13
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Water Chiller High Water Flow

    Quote Originally Posted by nike123 View Post
    Of course that chiller would not reach his set point when building load is higher then chiller capacity.
    I questioned that chiller will not reach set point when his capacity is higher then load, but flow thru evaporator is higher then nominal.
    At least, that is how I understood your post #7!

    I am with chillin here:
    that's more or less the same as I wrote!

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Water Chiller High Water Flow

    Quote Originally Posted by Lowrider View Post
    that's more or less the same as I wrote!
    Maybe I used wrong word (it is not my native language) or we have some miscommunication problem here.
    I ad some clarification in last post!

  15. #15
    Join Date
    May 2008
    Location
    UK
    Age
    53
    Posts
    8
    Rep Power
    0

    Re: Water Chiller High Water Flow

    The reason for the original post was we have had numerious compressor smash ups and what we have found is the flow rate is too high.
    I don't believe that too much water flow could or would cause liquid refrigerant returning back to the compressor causing it to smash up this is the debate we are having between us in the office. I do however believe the pressures would go up the delta T would go down and strugle to maintain the desired temp BUT not slug liquid back to the compressor to cause a smash up
    Regards Assad

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Water Chiller High Water Flow

    Quote Originally Posted by assadp View Post
    The reason for the original post was we have had numerious compressor smash ups and what we have found is the flow rate is too high.
    How much to high?

    I don't believe that too much water flow could or would cause liquid refrigerant returning back to the compressor causing it to smash up this is the debate we are having between us in the office. I do however believe the pressures would go up the delta T would go down and strugle to maintain the desired temp BUT not slug liquid back to the compressor to cause a smash up
    Regards Assad
    Delta T would go down depending on amount of raised flow. From my example above, it is obvious that this fall is not dramatic with some reasonable flow increase.

    Evaporation pressure will increase for corresponding difference in delta T of water in evaporator. If we have water temperature of 10°C then with dT of 5K we have evaporation temperature of 0°C and if we have dT of 3K then we have evaporation temperature 2°C. Maximum evaporation temperature with 10°C water in temperature should not exceed 5°C.
    That is not much rise in pressure, and chiller should not feel any consequence from that.

    At least, that is how I see relation of high flow of water in evaporator and pressure rise in refrigerant circuit from that!

    If I saying something wrong here, please someone, correct me.

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 01:25 PM
  2. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  3. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 07:14 PM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •