Scroll compressor on a VFD?
Been lurking on here for years, and usually find good answers to my questions. But haven't been able to find a discussion on using a VFD to control a scroll compressor. My plant has a system with four 5hp Copeland scrolls running two evaporators to chill seawater and I have a spare VFD. Anyone have a reason not to try running one unit on a VFD? Currently we control temperature by chilling to just below the target and then heating (oil-fired boilers) to our target temperature. This is to keep the temp at 5.5 degrees C +/- 0.2 degrees. Our chillers are currently on/off controlled and the temp swing is too great without the boilers running.
-
28-05-2008, 11:34 AM #2
Re: Scroll compressor on a VFD?
I would contact Copeland and see what they say. Copeland does have a Digital Scroll out, maybe some bearing difference between the two.
-
28-05-2008, 09:29 PM #3
Re: Scroll compressor on a VFD?
Copeland scrolls runs fine on a VFD. I think the limits is 35 to 75 Hz, maybe dependent on supply voltage. A phone to a suplier should confirm this.
-
28-05-2008, 11:58 PM #4
What a waste of energy, cooling and then reheating it to achiev a correct proces temperature.
We've done something similar and control it also within 0.2°C.
Cool as you say a small vessel like you do... 1 tot 2°C below desired proces temperature.
Install in the return line to the vessel a servo controlled 3 way valve which bypasses some warmer return water back to the colder outlet of the boiler.
You use this way the warmer return water to reheat a little bit.
The control signal comes from the outlet of the small vessel and this signal comes into a PID controller.
These valves with controller are available by Siemens/Staeffa Controls, Honeywell, .... and aren't not that expensive.
I think you can control your scroll from 35 Hz to 60 Hz, depends on the make.
Smilies suggested the digital scroll which is a very good alternative. But the compressors are in the machine I suppose.
I should invest the money in the 3 way valve instead of the VFD.Last edited by Peter_1; 30-05-2008 at 11:19 PM.
-
30-05-2008, 08:57 PM #5
Re: Scroll compressor on a VFD?
I agree on the waste of energy for controls. The price of oil is finally driving us to fix this. The 3 way valve sounds like a great solution. We have a spare VFD but with the price of oil and power, it's about time we did it right.
Similar Threads
-
Copeland Scroll Advanced Protection Problems
By dwayne in forum Trouble ShootingReplies: 8Last Post: 24-09-2010, 06:54 AM -
copeland ZR scroll vs VR scroll
By Lc_shi in forum Technical SpeculationsReplies: 7Last Post: 03-09-2008, 04:27 PM -
Hermetic reciprocating versus hermetic scroll
By Cofreth in forum Technical DiscussionsReplies: 26Last Post: 19-11-2005, 06:29 PM -
Scroll Compressor
By dwallan in forum CommercialReplies: 1Last Post: 30-07-2001, 04:18 AM