    Theoretical COP
    The link below provides a table relating to Daikins future refrigerant technologies.
    http://www.daikin.com/environment/in...luence_03.html
    Click - Types and properties of future refrigerants.(table) half way down the page.
    Ammonia (NH3) is stated as having a therotical COP (Relative to R22) of 107.
    What does this figure of 107 represent ?
    And in terms of energy output/input what is the ratio ?
    For example many domestic heat pump manufacturers state cop's as high as 5-1. (NIBE Fighter)
    Many thanks.
  2. #2
    Join Date
    Jul 2005
    Location
    Detroit,USA
    Age
    53
    Posts
    31
    Rep Power
    0
    Re: Theoretical COP
    It is probably a percentage. I did a quick calculation of the theoretical COP of both 22 and NH3 @ 0C evaporating, 45C condensing, 100% isentropic efficient compressors and I got:
    NH3 COP = 5.05
    R22 COP = 4.77
    so in this case, the NH3 COP was 106% that of R22
  3. #3
    Join Date
    Apr 2007
    Location
    Ireland
    Posts
    40
    Rep Power
    0
    Re: Theoretical COP
    Many Thanks. Very Helpful.
    Have just discovered the Heap Pump sub Forum also and finding it very informative.