    Theoretical COP



    The link below provides a table relating to Daikins future refrigerant technologies.
    http://www.daikin.com/environment/in...luence_03.html
    Click - Types and properties of future refrigerants.(table) half way down the page.

    Ammonia (NH3) is stated as having a therotical COP (Relative to R22) of 107.

    What does this figure of 107 represent ?
    And in terms of energy output/input what is the ratio ?
    For example many domestic heat pump manufacturers state cop's as high as 5-1. (NIBE Fighter)
    Many thanks.
    Last edited by Solair; 18-05-2008 at 10:08 PM.



  2. #2
    Join Date
    Jul 2005
    Location
    Detroit,USA
    Age
    52
    Posts
    31
    Rep Power
    0

    Re: Theoretical COP

    It is probably a percentage. I did a quick calculation of the theoretical COP of both 22 and NH3 @ 0C evaporating, 45C condensing, 100% isentropic efficient compressors and I got:

    NH3 COP = 5.05
    R22 COP = 4.77

    so in this case, the NH3 COP was 106% that of R22

  3. #3
    Join Date
    Apr 2007
    Location
    Ireland
    Posts
    40
    Rep Power
    0

    Re: Theoretical COP

    Many Thanks. Very Helpful.
    Have just discovered the Heap Pump sub Forum also and finding it very informative.

Similar Threads

  1. Advice For Students
    By Krups in forum Training
    Replies: 17
    Last Post: 15-07-2005, 10:03 PM
  2. PH diagram theoretical cycle
    By REL in forum Training
    Replies: 17
    Last Post: 11-12-2003, 03:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •