    cold store flooring preparation



    we are using vapor barriers etc for floor insulation. But recently I came across various materials being used for the same purpose. Also the scheme for doing all that is varying from suppliers to supplier. I was just wondering what forum members are doing on that
    Attached Files Attached Files



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: cold store flooring preparation

    Different materials might be used because someone is trying to save money, or trying to find a better method.

    My recommendation is to look at the perm rating of vapor retarder. Almost all vapor retarders will allow some moisture flow through them. So they way I see this is we need to use materials which offer the greatest resistance to moisture flow (lower perm rating).

    I believe this is one of the main reasons also for sub-floor heating. The warm sub-floor has a higher vapor pressure so that this drives the moisture out (so it can't freeze).
    If all else fails, ask for help.


  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: cold store flooring preparation

    The floor insulation should be made from the same material as the walls and just as thick with a vapor barrier and a concreet floor.

    No more and no less.

    Chemi

  4. #4
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: cold store flooring preparation

    smpsmp45
    We use polyethelene 150 micras . It is a good material. We overlaping the sheets more or less 10cm and seal with Protecapa from SIKA. This products are a very good vapor barrier but also do not have any olor. Many installer use sheet of paper impregnated with petroleum compound. This kind of products leaks bad olors to the cooldroom.
    The polyethelene film must seal must go at lest 50 cm agains the panels wall
    hope this helps
    regards
    Gwapa

Similar Threads

  1. Cold store Evaporator cleaning
    By hookster in forum System Optimization
    Replies: 12
    Last Post: 22-07-2008, 04:04 PM
  2. Replies: 15
    Last Post: 17-06-2008, 11:07 PM
  3. Expansion Joints in the cold store floor
    By smpsmp45 in forum NH3
    Replies: 2
    Last Post: 17-05-2008, 07:47 AM
  4. Cold Store Racking Design
    By Ashley in forum Ye Old Wifes Tales
    Replies: 11
    Last Post: 06-12-2007, 10:58 PM
  5. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Replies: 12
    Last Post: 16-11-2005, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •