    Low Pressure tripping



    Hi

    Any help would be appreciated, please be patient I'm still learning

    I have a problem with a chilling circuit that trips on low pressure.This is a basic 15 kw R407c system just comp, tev(ext equalised) Condenser and evap. There is a main fan which circulates air over the finned evap coil and another fan which circulates air over the finned condensing coil.( both fans are running ok) there are 2 tranducers for low and high side readings. The unit is tripping on low pressure switch ( set approx 2 bar)and judging by the readings this appears to be correct. The pipework from the tev and distributors to coils is frosted over.I thought maybe we had a leak ( short of gas or tev partially blocked ?)
    According to the on site info the system charge is 6kg r407c.I recovered the gas into a recovery cylinder which weighs in at 5kg....would that cause the prob?
    Appologies for the grammer and spelling , any further info ( what bit I know ) will gladly be made available.System running readings were :-

    low side = around 2 bar but trips
    hight side = around 9 bar.
    Room temp = 28 c
    outside temp = 16

    Hope I've made sense

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by Beginner View Post
    According to the on site info the system charge is 6kg r407c.I recovered the gas into a recovery cylinder which weighs in at 5kg....would that cause the prob?

    Thanks
    Of course that 17% less refrigerant will cause the problem. More in to that is, that this refrigerant is blend of 3 components with high temperature glide (7K).
    Now, not only that you have less refrigerant then required, but you also have unknown composition of components.
    Last edited by nike123; 17-05-2008 at 12:41 AM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Low Pressure tripping

    Hi and welcome to the forum.

    Your spelling looks OK so don't hide in the corner yet...

    Well if you took out 5kg and there should be 6kg it appears that 1kg has escaped.

    This means that there is a leak somewhere, all you have to do now is find it and fix it. Sounds easy but probably won't be.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    May 2008
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Low Pressure tripping

    Hi

    Thanks for the replies. May I ask another quick question? Yes?...ok..lol

    What would be the differing symptoms in terms of high and low side pressures of :-
    1.....low charge
    2.....restricted tev

    Thanks any help is appreciated.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Low Pressure tripping

    Quote Originally Posted by Beginner View Post
    What would be the differing symptoms in terms of high and low side pressures of :-
    1.....low charge
    2.....restricted TEV
    Thanks any help is appreciated.
    Low charge = low LP and low HP
    Restricted TEV = Low LP and and low HP (low load to the condenser) but higher HP then when low on charge (liquid will back up in the condenser)
    Less or more normal HP.

    More important low charge = high SH and low SC
    Restricted TEV = high SH but very high SC (the high SC is the biggest difference)

    Decomposition of the R407c due to the leak is possible.
    SI there something to control Hp (fan controlled by HP?) Your HP seems very low for an ambient of 16°C outside.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low Pressure tripping

    Quote Originally Posted by Beginner View Post
    Hi

    Thanks for the replies. May I ask another quick question? Yes?...ok..lol

    What would be the differing symptoms in terms of high and low side pressures of :-
    1.....low charge
    2.....restricted tev

    Thanks any help is appreciated.
    Differing is that, when we have restriction at TEV, we experience lot of subcooling in the condenser, which is not the case with low charge.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Low Pressure tripping

    Nike 123, we're exactly on the same line.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low Pressure tripping

    Where is delete button???

    Last edited by nike123; 17-05-2008 at 06:15 PM.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low Pressure tripping

    Quote Originally Posted by Peter_1 View Post
    Nike 123, we're exactly on the same line.
    Yep, i saw that you already posted same answer when I pressed submit reply button!

    Newer mind, this way, message is twice stronger!

  10. #10
    Join Date
    May 2008
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Low Pressure tripping

    Thanks all for replies. Can I also ask how for each case ( low charge and restricted tev ) the discharge side is affected.
    Thanks

  11. #11
    Join Date
    May 2008
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Low Pressure tripping

    oops ..missed a word out there ,,,,should have said discharge side temperature in each case...thanks

  12. #12
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Low Pressure tripping

    Hi beginner,
    for a start, i'll connect external pressure gage on high, low & oil path for better readings.

    next, i'll run the system with few guys standing at different points to observe each equipment esponse.

    and, if the lo press trip too fast, i'll check from liquid supply line downwards until comp suction port.
    otherwise, i'll increase refrigerant charge to allow me longer hours to identify the possible cause.


    hope that helps.

    hendry, on wesak day holiday.
    Hendry

    "What uncertainty means to you, and you only?"

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Low Pressure tripping

    Quote Originally Posted by Beginner View Post
    oops ..missed a word out there ,,,,should have said discharge side temperature in each case...thanks
    Well, in both cases because the evaporator is underfeed, you will have a high SH, so high to very high discharge temperatures. This is the same for both.
    You can see this in a log/P chart
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    May 2008
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Low Pressure tripping

    Hi

    Now this is were I get confused ....I thought because little gas getting through tev = high superheat but I also thought maybe little gas = low duty and therefore low load so no gas to compress so lower discharge temps...put me out of my misery someone...lol...thanks

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low Pressure tripping

    Quote Originally Posted by Beginner View Post
    Hi

    Now this is were I get confused ....I thought because little gas getting through tev = high superheat but I also thought maybe little gas = low duty and therefore low load so no gas to compress so lower discharge temps...put me out of my misery someone...lol...thanks
    http://www.hvacwebtech.com/1marks.htm

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Low Pressure tripping

    Or the PPP at http://www.hvac-pro.org/articles/superheat.pps

    Your question goes back to the real basics of a log/p chart.
    Without the intention to being rude or to humiliate you, I'm sure nobody ever learned you how a log/P chart works.
    As long as you don't really understand this, there will always be gaps and faults in your way of thinking.

    But your first post and your nickname says you're a beginner and these are normal questions but you surely should take some time to read a good book which explains the beginning of cooling process and more specific the log/p chart.

    I suggest that you read once Roy Dossat's book which is a very good start.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    May 2008
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Low Pressure tripping

    Ok thanks for your patience

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •