    Old York Control wiring diagram



    Hi all
    anyone have the colour meaning for a Old York reverse Cycle split ducted unit
    trying to replace the original thermostat control with a new Honeywell Focus Pro TH5110D

    Heres a pic of the outdoor unit control board
    http://s291.photobucket.com/albums/l...5081652-02.jpg

    The wire thats got me puzzled is the piont-O on the out door board its the one with the thicker white wire

    This is what is on the out door board

    anyone able to let me know if this is correct? PLease

    (w)= white = heat relay?
    (r) = red = 24vac power from heating?
    (y) = yellow =Comp Contactor?
    (b) = Black 24vac Common?
    (o) = white (thick) 24vac power from cooling?
    Last edited by Makanic; 15-05-2008 at 04:19 PM. Reason: Added more details



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Old York Control wiring diagram

    W,R,Y,B are as you say, if memory serves me i think O was for controlling the 4 way valve?

    Al

  3. #3
    Join Date
    May 2007
    Location
    Australia
    Age
    39
    Posts
    73
    Rep Power
    18

    Re: Old York Control wiring diagram

    Quote Originally Posted by al View Post
    W,R,Y,B are as you say, if memory serves me i think O was for controlling the 4 way valve?

    Al
    The Honeywell has theses pin outs

    TH5110D

    (Rc)=Linked to (r)
    (r)=24vac power from heating
    (y)=Compressor contactor
    (c)=24vac Common (for 2 transformer systems use common wire from cooling transformer)
    (w)=heat relay or (o) - (b)
    (g)=Fan relay

    (w) can be wired with (y) ?

    York controler

    (w)= white = heat relay
    (r) = red = 24vac power from heating
    (y) = yellow =Comp Contactor
    (b) = Black 24vac Common
    (o) = white (thick) Reversing

    I am trying to answer my own questiions ...
    Am i on the right track..? anyone able to let me know if this is correct? PLease

    Thanks in advance
    Last edited by Makanic; 16-05-2008 at 02:32 AM. Reason: added stuff

  4. #4
    Join Date
    Jun 2006
    Location
    USA
    Age
    63
    Posts
    10
    Rep Power
    0

    Re: Old York Control wiring diagram

    Quote Originally Posted by Makanic View Post
    The Honeywell has theses pin outs

    TH5110D

    (Rc)=Linked to (r)
    (r)=24vac power from heating
    (y)=Compressor contactor
    (c)=24vac Common (for 2 transformer systems use common wire from cooling transformer)
    (w)=heat relay or (o) - (b)
    (g)=Fan relay

    (w) can be wired with (y) ?

    York controler

    (w)= white = heat relay
    (r) = red = 24vac power from heating
    (y) = yellow =Comp Contactor
    (b) = Black 24vac Common
    (o) = white (thick) Reversing

    I am trying to answer my own questiions ...
    Am i on the right track..? anyone able to let me know if this is correct? PLease

    Thanks in advance

    You are mostly right. The W out on the Stat does NOT get tied to the air handler, if you do you will open a can of worms. if you tie it to the W terminals in the air handler the heat strips will stay on all the time the stat switch is on heat. It would be tied to the W input on the newer York HP unit, on the older unit it will not be used. The W output on the outdoor unit will go to the W1 and W2 terminals of the air handler to supply supplemental heat when the unit goes into defrost. The O in the stat goes to the O in the outdoor unit to enegize for heat mode, defaut operation is cool mode.Then you have R, C and Y, 24 volt hot, common and Cool respectivly. I was York tech support for several years, I am now support for Ruud/Rheem. if I can be of any further help just let me know...

Similar Threads

  1. York Wiring Diagrams
    By iceman007 in forum Trouble Shooting
    Replies: 14
    Last Post: 10-04-2010, 06:48 PM
  2. Daikin VRV electrical wiring
    By anracau in forum Air Conditioning
    Replies: 13
    Last Post: 26-11-2009, 04:55 PM
  3. Wiring diagram
    By plumtech in forum Refrigerants
    Replies: 1
    Last Post: 29-04-2008, 02:21 PM
  4. Control Wiring Shielded both ends
    By Husky250 in forum Air Conditioning
    Replies: 9
    Last Post: 05-04-2008, 04:10 PM
  5. Re: control wiring confussion
    By IBAD HANTEX in forum Electrical
    Replies: 0
    Last Post: 24-03-2008, 10:35 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •