    TEV for 3-banger chiller?



    We have been griping about the inability to apply an expansion valve in the CPU, VC, and chipset cooling applications. But in considering Bowman 1964's 3-evap single system design, I decided that if we attribute a 150w load for each evaporator (450btuh approx.), times 3 evaps = 450w (1,350 btuh) or .1125 tons.....

    Guess what.... that's right in the ballpark for a Sporlan EF-1/8 expansion valve.




  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Give or take a little. One TEV controlling 3 separate evaporators?
    Prof Sporlan

  3. #3
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Think of it as a multiple circuit evaporator. Perhaps a properly sized distributor would be called for, but I'd whip it together before I called the plant to spec one for me.

    The evaps will be on a common suction, therefore NOT "seperate"

    i might consider piping in series. The valve would definitely be externally equalized, because I would imagine a pretty good pressure drop through the tiny evaporator(s) circuit.

    The low pressure connections between the blocks (evaporators), merely think of as return bends on a fan coil.

    (the evaps/blocks are no more that 6" away from each other)


    OH!!!! .... Professor, I placed that order today. I was told it would be 3 to 4 weeks from the plant for my EFSE-1/8-ZP expansion valve. Could you go out on the floor, and tell the guys to put roller skates on it? LOL!!!
    Last edited by herefishy; 10-09-2003 at 02:52 AM.

  4. #4
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    52
    Posts
    34
    Rep Power
    0

    Re: TEV for 3-banger chiller?

    You could try mounting a low pressure reciever/suction accumalator on the outlet of the evapourators with a common suction which you control the superheat on?

  5. #5
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: TEV for 3-banger chiller?

    I've seen a few folks try to run 2 or three evaps in parallel from one TXV with limited success. The problem is the ability to feed the coils correctly under all conditions. Unless you have some sort of distributir, the feed will be very problematic at best.

    Ken

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •