    R134a for Low temperatures



    Hi all,

    I have a question regarding use of R134a in a freezer. The compressor manufacturer's specs indicate a lowest evap temp (-) 35°C. At this temp, the suction pressure will be at something like 9 psia or about (-) 6 psig. Is there any problem with a system that operates at such low pressures in the long run ?? Can somebody throw light on this ??



  2. #2
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: R134a for Low temperatures

    obviously R404A would be better but R134A is similar to the old R12 and there were enough running away happily on that,most domestic freezers were on it too,low pressure should not be a problem unless it drops into a vacum then theres oil trouble.

  3. #3
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25

    Re: R134a for Low temperatures

    You must be talking of a domestic system, in a commercial applicaion there are much more favourable refrigerants, like r404a or r507.

    I have serviced freezers on r12 and its replacements and found that you pretty much need to run a vacuum to acxhieve the desired SST (-35 as you have stated). I'm not sure that oil is a problem in a vacuum... that is the first I have heard of that, a vacuum - as in 10 inches of mercury is merely a form of reading pressure, yes it is below atmospheric pressure but as the system is not open to atmospheric pressure everything will operate fine provided there are no leaks - then air will be sucked in. There are plenty of systems that run vacuums to achieve desired conditions especially in low temp industrial on NH3 and centrif liquid chillers, most contain auto air purgers incase of air ingress though.
    ...and she said "give it to me you big fridgie"

  4. #4
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: R134a for Low temperatures

    i've seen a few refeer units on R13A at low temp (-20 deg C).

    Not sure why this is? or why it should not be?

    Apart from the obviuos vacuum issue ! Any thoughts anyone?

    Billy ray

  5. #5
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: R134a for Low temperatures

    Quote Originally Posted by umeshuv View Post
    Is there any problem with a system that operates at such low pressures in the long run ?? Can somebody throw light on this ??
    umeshuv,

    If this compressor you have is listed as a LT R134a unit then it's ok to run it in the operating range listed by the manufacturer. Just watch the capacity because it drops quite a bit as the SST drops.

    If it's a R404A compressor and you just want to use R134a then it wouldn't be advisable.

    Many old low temp R-12 freezer systems ran in a vacuum with no problem.

  6. #6
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: R134a for Low temperatures

    most of the old systems on R12 low temp used to run just above 0 psi,if they were set up propely and running correctly not in a vac,were talking old stuff here and in a lot of cases old semi hermetics ,i found anyway that if they had run short of gas or running in a vac for other reasons that after a time a good percentage of the compressor oil had been laying elsewere in the system,once it was running right again it would start returning to the compressor. how many times have you been to a job where the system has lost its gas and theres no oil in the sight glass ! running in a vac is just that,yes you might get the system to balance but its not good practice. thats how i see it anyway.

  7. #7
    Join Date
    Dec 2007
    Location
    USA
    Posts
    13
    Rep Power
    0

    Re: R134a for Low temperatures

    I don't like the idea that the system would operate in a vacuum on the low side.

    I heard some brazing solders are prone to leakage in R134 (Sil Phos? -- don't remember).

  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: R134a for Low temperatures

    Anyone else here have the priviledge of refitting old r12 open drive systems for freezers to r134a?
    Bloody nightmare, had to babysit that thing due to it running in a vacuum, checking the oil to make sure it all doesn't disappear.
    Not to mention the fact it was open drive and is in a vacuum you never know what's going to happen with a crankshaft seal on r134a (we had a few failures on higher temp open drives after charging with r134a).
    Domestics seem to run OK for some reason, most don't run in a vacuum anyway, maybe oversized evap, shorter capillary?
    But putting r134a and TXV into a freezer design for r12 meant it would run in a vacuum most of the time. We had to make sure it never got below -16C in the freezer if we didn't want to babysit it or have any problems, it broke down every month otherwise, usually on a friday afternoon.
    Last edited by paul_h; 18-09-2008 at 08:02 PM.

  9. #9
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: R134a for Low temperatures

    Quote Originally Posted by old gas bottle View Post
    obviously R404A would be better but R134A is similar to the old R12 and there were enough running away happily on that,most domestic freezers were on it too,low pressure should not be a problem unless it drops into a vacum then theres oil trouble.
    what are these oil troubles by the way...

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 01:39 PM
  2. flow switch connection
    By afeef in forum The Trail of Tears
    Replies: 18
    Last Post: 23-12-2009, 07:55 PM
  3. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 01:44 AM
  4. Replies: 5
    Last Post: 01-03-2004, 10:59 PM
  5. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •