Thread: PHE as condenser
-
12-05-2008, 05:19 AM #1
PHE as condenser
Hi everybody,
I was wondering if anyone used a Plate Heat Exchanger as water cooled condenser?
If so, what about scaling?
I would appreciate any comments.
Cheers
Even Einstein Asked Questions
-
12-05-2008, 08:47 AM #2
Re: PHE as condenser
One of our customers is using these PHE. I shall get his feedback on this.
-
12-05-2008, 11:22 AM #3
Re: PHE as condenser
As long as the condensing circuit is a closed circuit, no scaling is produced. I've used a lot of those without problems.
-
12-05-2008, 10:38 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: PHE as condenser
Closed circuit is the way!
-
13-05-2008, 02:37 AM #5
-
13-05-2008, 02:51 AM #6
Re: PHE as condenser
Hi lana.
Depending on capitol equipment costs a cooling tower may be less expensive than an evaporative fluid cooler. I think the piping costs for either would be similar. However, if you look at life cycle costs including maintenance the evaporative fluid cooler may be less. The need to regularly clean strainers for the PHE circuit would be eliminated, while the chemical treatment should be similar for either case (in the evaporative sections of the heat rejection device).
Closed circuit would be preferable I think for the PHE, but the above are my wondering thoughts on how you might justify either one.
Hope things are well with you and your family.If all else fails, ask for help.
-
13-05-2008, 04:42 AM #7
Re: PHE as condenser
Hi everybody,
Thank you for your replies.
What I was wondering is actually an open circuit with a cooling tower. Obviously if the water circuit was closed then the scaling would be minimal.
Because of narrow passage ways between the plates, If scaling occurs then ....
On the other hand if the condenser is acid washed then those scales could not get out.
Thanks again.
CheersEven Einstein Asked Questions
-
14-05-2008, 07:48 AM #8
Re: PHE as condenser
I checked with the customer on this aspect. They are openign up the Condenser once in a year & are doing the cleaning operation. Inspite of all the precautions, they still find small particles which sip in through the filter though. But in general they are happy about it.
-
14-05-2008, 08:20 AM #9
Re: PHE as condenser
Even with a tds (total disolved solids)controller and regular water treatment scale will still occur when used with a cooling tower , some of the bphe scaled within 3 years on one of our sites , the tube in tube copper ones seemed to last a little longer but are only good for small units
-
14-05-2008, 09:17 AM #10
Re: PHE as condenser
hi all, i was on a job where we had 154 units manufactured by denco and they all had plate heat exchangers,individual units upto 105 kw cooling with three circuits.
but the system was a primary and secondary type, primary being cooling towers and huge plate heat enchangers and secondary being the flow and return to and from the building.worked fine because the water in the secondary was very clean.
uniflair also make these units which have plate heat exchangers as standard.hope this helps.
-
16-05-2008, 08:10 AM #11
Re: PHE as condenser
Hi there,
Thank you everybody for your replies.
Personally I would prefer shell and tube condensers and also PHE which is the gasket type (can be opened). BUT the brazed type ......
Most appreciated guys.
CheersEven Einstein Asked Questions
-
17-05-2008, 09:56 AM #12
Re: PHE as condenser
Hello!
I also had situation with PHE and open system. But there are no problems in this case. Customer cleans this PHE ones a year.
-
18-05-2008, 04:20 AM #13
Re: PHE as condenser
Hi Iana,
knowing the high requriement necessary in PHE design, normally it is not advisable to use it in condensing pack.
moreover, its maintenance at the mercy of plant owner.
i feel the operation cost should be the key considerations.
hope that helps.
Hendry, on wesak day holiday.Hendry
"What uncertainty means to you, and you only?"
-
18-05-2008, 09:50 AM #14
Re: PHE as condenser
Thanks for the input.
CheersEven Einstein Asked Questions
-
19-05-2008, 12:14 AM #15
Re: PHE as condenser
Hi hendry,
It's not Wesak day is it just had a beer with my dinner
Jon
edit: just checked and it is too, still i've only broken two of the eight preceptsLast edited by monkey spanners; 19-05-2008 at 12:19 AM.
-
30-07-2008, 09:37 AM #16
Re: PHE as condenser
PHE is not suitable for open cooling water system, maybe dust filter and water treatment such as water softening be used .
Similar Threads
-
Plate Heat Exchagers - Condenser
By Billy Ray in forum Technical DiscussionsReplies: 9Last Post: 11-05-2008, 06:16 PM -
method to design air cooled condenser
By abbasi in forum New TechnologiesReplies: 4Last Post: 12-02-2008, 08:34 AM -
Optimum condenser fan speed
By star882 in forum FundamentalsReplies: 4Last Post: 27-02-2006, 01:50 AM -
Cooling condenser of split with condensate from evaporator
By smileypete in forum Air ConditioningReplies: 11Last Post: 10-07-2005, 08:21 AM -
Condenser Fan
By Vicky in forum Supermarket RefrigerationReplies: 3Last Post: 20-04-2005, 08:38 AM