    PHE as condenser



    Hi everybody,

    I was wondering if anyone used a Plate Heat Exchanger as water cooled condenser?
    If so, what about scaling?

    I would appreciate any comments.

    Cheers


    Even Einstein Asked Questions

  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: PHE as condenser

    One of our customers is using these PHE. I shall get his feedback on this.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: PHE as condenser

    As long as the condensing circuit is a closed circuit, no scaling is produced. I've used a lot of those without problems.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: PHE as condenser

    Closed circuit is the way!

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: PHE as condenser

    Quote Originally Posted by lana View Post
    Hi everybody,

    I was wondering if anyone used a Plate Heat Exchanger as water cooled condenser?
    If so, what about scaling?

    I would appreciate any comments.

    Cheers
    Most chiller manufacturers also include or recommend the use of minimum 100micron mesh filter in the field piping to protect the very narrow waterways in the PHE.
    If in doubt read the instructions. If still in doubt follow them.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: PHE as condenser

    Hi lana.

    Depending on capitol equipment costs a cooling tower may be less expensive than an evaporative fluid cooler. I think the piping costs for either would be similar. However, if you look at life cycle costs including maintenance the evaporative fluid cooler may be less. The need to regularly clean strainers for the PHE circuit would be eliminated, while the chemical treatment should be similar for either case (in the evaporative sections of the heat rejection device).

    Closed circuit would be preferable I think for the PHE, but the above are my wondering thoughts on how you might justify either one.

    Hope things are well with you and your family.
    If all else fails, ask for help.


  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: PHE as condenser

    Hi everybody,

    Thank you for your replies.

    What I was wondering is actually an open circuit with a cooling tower. Obviously if the water circuit was closed then the scaling would be minimal.
    Because of narrow passage ways between the plates, If scaling occurs then ....
    On the other hand if the condenser is acid washed then those scales could not get out.

    Thanks again.
    Cheers
    Even Einstein Asked Questions

  8. #8
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: PHE as condenser

    I checked with the customer on this aspect. They are openign up the Condenser once in a year & are doing the cleaning operation. Inspite of all the precautions, they still find small particles which sip in through the filter though. But in general they are happy about it.

  9. #9
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: PHE as condenser

    Quote Originally Posted by lana View Post
    Hi everybody,

    Thank you for your replies.

    What I was wondering is actually an open circuit with a cooling tower. Obviously if the water circuit was closed then the scaling would be minimal.
    Because of narrow passage ways between the plates, If scaling occurs then ....
    On the other hand if the condenser is acid washed then those scales could not get out.

    Thanks again.
    Cheers
    Even with a tds (total disolved solids)controller and regular water treatment scale will still occur when used with a cooling tower , some of the bphe scaled within 3 years on one of our sites , the tube in tube copper ones seemed to last a little longer but are only good for small units

  10. #10
    Join Date
    Apr 2008
    Location
    east london uk
    Posts
    9
    Rep Power
    0

    Re: PHE as condenser

    hi all, i was on a job where we had 154 units manufactured by denco and they all had plate heat exchangers,individual units upto 105 kw cooling with three circuits.
    but the system was a primary and secondary type, primary being cooling towers and huge plate heat enchangers and secondary being the flow and return to and from the building.worked fine because the water in the secondary was very clean.
    uniflair also make these units which have plate heat exchangers as standard.hope this helps.

  11. #11
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: PHE as condenser

    Hi there,

    Thank you everybody for your replies.

    Personally I would prefer shell and tube condensers and also PHE which is the gasket type (can be opened). BUT the brazed type ......

    Most appreciated guys.

    Cheers
    Even Einstein Asked Questions

  12. #12
    Join Date
    Sep 2007
    Location
    Ukraine
    Age
    39
    Posts
    17
    Rep Power
    0

    Re: PHE as condenser

    Hello!

    I also had situation with PHE and open system. But there are no problems in this case. Customer cleans this PHE ones a year.

  13. #13
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: PHE as condenser

    Hi Iana,
    knowing the high requriement necessary in PHE design, normally it is not advisable to use it in condensing pack.
    moreover, its maintenance at the mercy of plant owner.
    i feel the operation cost should be the key considerations.

    hope that helps.

    Hendry, on wesak day holiday.
    Hendry

    "What uncertainty means to you, and you only?"

  14. #14
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: PHE as condenser

    Thanks for the input.
    Cheers
    Even Einstein Asked Questions

  15. #15
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: PHE as condenser

    Hi hendry,

    It's not Wesak day is it just had a beer with my dinner


    Jon

    edit: just checked and it is too, still i've only broken two of the eight precepts
    Last edited by monkey spanners; 19-05-2008 at 12:19 AM.

  16. #16
    Join Date
    Aug 2006
    Location
    China
    Age
    55
    Posts
    52
    Rep Power
    18

    Re: PHE as condenser

    PHE is not suitable for open cooling water system, maybe dust filter and water treatment such as water softening be used .

Similar Threads

  1. Plate Heat Exchagers - Condenser
    By Billy Ray in forum Technical Discussions
    Replies: 9
    Last Post: 11-05-2008, 06:16 PM
  2. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  3. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM
  4. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM
  5. Condenser Fan
    By Vicky in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 20-04-2005, 08:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •