    Re: Carrier Transicold Container Problem

    Quote Originally Posted by paulo almeida View Post
    for trucs
    I've got a few older ones stashed on a CD somewhere.
    Got a model number ?

  2. #2
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: Carrier Transicold Container Problem

    hi there. I have had this problem before as well. the first thing to check is the fuses on the front of the controller. (F1 ,F2) the alarm code tells you that one of these fuses has blown. relace fuse and start up the box. If the box is turned back on and tha alarm light is still active then go into the alarm list and make sure the alarm hasn't gone from AA status to IA21. Once it has gone IA the alarm can be cleared. If it blows again. check the control transformer voltage to the controller..... hope this helps

  3. #3
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: Carrier Transicold Container Problem

    its the SMV module shorting to ground underneath the quench valve. from the factory they install the module so the water that drips off the quench valve right into the wiring. hope this helps.

  4. #4
    SGTChee's Avatar
    SGTChee Guest

    Re: Carrier Transicold Container Problem

    Hello all, im currently out in the middle of no where in afganistan and I came across a Carrier transicold container with a alarm code AL15, so i read thru the manual and it tells me nothing of that code. the model is 60NT40-541-302. if anyone can tell me why this container is shutting off and displaying AL15 that would be great.

  5. #5
    SGTChee's Avatar
    SGTChee Guest

    Re: Carrier Transicold Container Problem

    sorry back again the model number is 69NT40-541-302.....a 9 instead of a 0

  6. #6
    SGTChee's Avatar
    SGTChee Guest

    Re: Carrier Transicold Container Problem

    ok I looked at it somemore, for one there is 543Volts coming in, and 9 amps on each leg, the quench valve is frosting over and there is a major temp difference on the filter dryer. the unit is getting power from the generator that hooks up to it on top. when the unit goes into cool mode the temp dose not go lower than 73 degrees F. All pre-trip codes pass except (auto2 mode) under P8-1 this comes up as a fail.

  7. #7
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: Carrier Transicold Container Problem

    Quote Originally Posted by SGTChee View Post
    ok I looked at it somemore, for one there is 543Volts coming in, and 9 amps on each leg, the quench valve is frosting over and there is a major temp difference on the filter dryer. the unit is getting power from the generator that hooks up to it on top. when the unit goes into cool mode the temp dose not go lower than 73 degrees F. All pre-trip codes pass except (auto2 mode) under P8-1 this comes up as a fail.
    hi sgtchee

    have you check refrigeration level??

    al15 is loss of cool..reefr units haven t got good performans..

    i think refrigaration level is no good..

    also txv is not good workşng?*you have to check its..is there to much ice on the suction pipe??If there is too much ice on cuction pipe txv is not good working

    im waiting ur reply..

    see you

    reefer mechanic..

  8. #8
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: Carrier Transicold Container Problem

    Quote Originally Posted by SGTChee View Post
    and there is a major temp difference on the filter dryer.
    Ding, ding, ding, ding.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier Transicold problem
    By tsvetomir in forum Transport
    Replies: 17
    Last Post: 16-08-2010, 02:59 AM
  3. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •