Re: Carrier Transicold Container Problem
alarm 20,fuse 3 blown,10ampere, 69nt40-501 this is the scenario, i see alarm 20 in my unit so i change the 10ampere fuse 3, but again the fuse is blown again and again.... i'm having the same exact problem, whAT can i do? can you help me? carlosluisfs@hotmail.com
-
20-01-2012, 11:13 PM #3
Re: Carrier Transicold Container Problem alarm 56
Hi all... I have a problem with rts sensor(3 wires)...the controller gives alarm 56, i have change the sensor with an new one, i have done P-5, and it fails 5-2 and keep showing
alarm 56, i've change the controller and it happening the same try with another new sensor nothing change always alarm 56.
I have checked the Continuity of the wires and its OK.
Can it have any conflict with any other sensor of the unit??
Anyone can help me with this stress problem?
I have nightmares with Alarm 56?..please help
Thanks all
-
23-01-2012, 11:23 PM #4
Re: Carrier Transicold Container Problem alarm 56
Problem solved
the problem was in the controller pins Where the wires of the probe connect...
Thanks all
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Carrier Transicold problem
By tsvetomir in forum TransportReplies: 17Last Post: 16-08-2010, 02:59 AM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
York Chiller Excessive Purges Problem
By imranmd in forum CommercialReplies: 5Last Post: 07-03-2008, 05:13 AM