    Plate Heat Exchagers - Condenser



    Plate Heat Exchangers for Condenser Purpose?

    Thoughts / Suggestions / Required Please - - -

    When applying a plate heat exchanger as a condenser, what considerations are required?

    The application is medium temperature (+4 Cold Room).

    The condenser is a plate heat exchanger, which is connected to a central building systems evaporative cooling tower. The condenser receives water at typically +25 deg C (this dependant on the ambient).

    All thoughts & suggestions on configuration are wellcome, more particular is the requirement for a liquid receiver?

    Note: The liquid main length is 1 meter (water cooled condening unit positioned above cold room).

    Billy Ray



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Plate Heat Exchagers - Condenser

    Right or wrong place, doesn't matter to me!

    I work on a lot of chillers with water cooled condensors using either a PHE or shell and tube.

    The big advantage of a PHE is the smaller space needed compared to a shell and tube in the smaller chillers.

    In the scroll chillers we use PHE's, in the larger chillers (screw and centrifugals) we use shell and tube because here a phe would be larger than a shell and tube.

    Hope I explained it clearly!

    The need to control the entering water temperature remains the same for each condensor.

  3. #3
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Plate Heat Exchagers - Condenser

    Lowerider,

    do you regonise a need for a liquid receiver when utilizing a PHE?

    in contary, a shell & tube condenser can be considered as a combined condenser/receiver!

    Billy Ray

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Plate Heat Exchagers - Condenser

    That all depends what type of system you use.

    It depends on how much you'll have to buffer. In a phe the amount you can buffer is smaller than in a shell and tube.

    On our chillers we only use a buffer if it's a heat pump, not when it's a chiller.

    If you have a cold store with multiple evaps than the need for a buffer will be bigger than on the chillers we build. You'llhave to calculate the amount of refrigerant circulating at full load and at the lowest load and size the buffer to match the difference.

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Plate Heat Exchagers - Condenser

    Also if its on pumpdown control you will need enough storage capacity for it to pumpdown fully.

    Jon

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Plate Heat Exchagers - Condenser

    Since the volume of the PHE is a lot lower than the shell & tube you will probably need a receiver because of the pump down cycle and longer line lengths in a cold store.

    The requirements for a PHE are the same as for a shell & tube exchanger. You just select the PHE for the heat rejection requirements, water flow rates (or water temperatures IN & OUT, which will determine the flow rate for the heat rejection necassary), condensing temperature desired, etc.
    If all else fails, ask for help.


  7. #7
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Plate Heat Exchagers - Condenser

    I'll add that a brazed PHE is more difficult to clean versus a shell and tube. Keep the water clean.

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Plate Heat Exchagers - Condenser

    Quote Originally Posted by powell View Post
    I'll add that a brazed PHE is more difficult to clean versus a shell and tube. Keep the water clean.
    You're right! That's why we always say the water circuit has to be be flushed a couple of times after installation and there has to be a filter included!

  9. #9
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Plate Heat Exchagers - Condenser

    Any suggestion for filter basket size?

    500 micron / 1000 micron?

    'Too small' i would suggest would continually block, bearing in mind if the system was hooked up to an evaporative tower on a central system, maybe not so much if connected to a dry cooler!

    'Too big' would not protect!

    Billy Ray

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Plate Heat Exchagers - Condenser

    Or, you can use a centrifugal separator with a blow down cycle. No filters to clean and it's automatic.
    If all else fails, ask for help.


Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Replies: 10
    Last Post: 18-07-2007, 08:07 AM
  5. Efficient Water-Source Condenser Design?
    By Enginerd in forum Fundamentals
    Replies: 4
    Last Post: 28-05-2007, 05:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •