    Cold store Evaporator cleaning



    Hello All
    I have a client that is addamant that his cold store evaporators do not require a regular cleaning (I have atated a minimum yearly with twice yearly recommended)
    The evaporator coils are very dirty as enviroment is dirty and majority of product is cardboard packaged.
    Stores vary between 14 and 4 DegC holding temp.
    I would like some information on efficiency reduction and if possible a way of determining the reduction in efficiency of the evaporators due to build up.
    What is recommended cleaning?



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Cold store Evaporator cleaning

    Quote Originally Posted by hookster View Post
    Hello All
    I have a client that is addamant that his cold store evaporators do not require a regular cleaning (I have atated a minimum yearly with twice yearly recommended)
    The evaporator coils are very dirty as enviroment is dirty and majority of product is cardboard packaged.
    Stores vary between 14 and 4 DegC holding temp.
    I would like some information on efficiency reduction and if possible a way of determining the reduction in efficiency of the evaporators due to build up.
    What is recommended cleaning?
    Sorry hookster.
    I am with the client on this one!
    Grizzly

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Cold store Evaporator cleaning

    And I'm going to take the opposite approach Grizzly. I have seen a lot of coils coated in dirty cardboard dust that once wetted turns into mud.

    Twice a year cleaning is a little extreme, once a year is questionable, but once every five years or so I think is reasonable. But then, it depends on the rate of accumulation too.

    I've seen coils that had never been cleaned, but once every five years or so should be acceptable as part of preventive maintenance. If they were put on a rotating schedule the coils could be cleaned one at a time over the span of a year.

    The only way I know how to estimate the difference is to look at the suction pressure currently running and what it should be.
    If all else fails, ask for help.


  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Cold store Evaporator cleaning

    One of our clients runs an agg packing wharehouse and thier maintenanace staff would wash out the evaporators every few months due to the cardboard dust in the air.
    And another customer who made pre packed sandwitches used to have us clean the evaporators once or twice a year due to dust from those blue paper towels blocking the evaporator.

    I think they would be a bit like condensers in that it would be easier to keep them clean than clean one once its become blocked with cr*p. On a cellar cooler once we had to remove the evaporator outside so that we could pressure was all the black mouldy stuff out of it, would have been cheaper to keep it clean in the first place.

    Jon

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Cold store Evaporator cleaning

    Quote Originally Posted by US Iceman View Post
    And I'm going to take the opposite approach Grizzly. I have seen a lot of coils coated in dirty cardboard dust that once wetted turns into mud.

    Twice a year cleaning is a little extreme, once a year is questionable, but once every five years or so I think is reasonable. But then, it depends on the rate of accumulation too.

    I've seen coils that had never been cleaned, but once every five years or so should be acceptable as part of preventive maintenance. If they were put on a rotating schedule the coils could be cleaned one at a time over the span of a year.

    The only way I know how to estimate the difference is to look at the suction pressure currently running and what it should be.

    Please read the post again

    "I have a client that is addamant that his cold store evaporators do not require a regular cleaning (I have atated a minimum yearly with twice yearly recommended)"

    Even your statement could not be construed as regular cleaning.
    I also have many years Cold store experiance and agree that in unusual circumstances more regular cleaning is required.
    And I totally agree with both you and taz.
    But I still disagree that in normal circumstances twice a year is the required frequency.
    Maybe I did not clarify what I ment.
    Basically I agree with your statement but don't read into mine what was never there in the first place.
    Grizzly
    Ps Your turn to rant now mate!

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Cold store Evaporator cleaning

    I suppose the question i should have asked is "Is the coil in a dirty environment and gets blocked quickly?"

    As Grizzly points out many evaporators in clean environments run for many years without needing cleaning.

    Jon

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Cold store Evaporator cleaning

    I would sugest they just be cleaned as required when the condensers are cleaned just have a butchers and show the customer when the crap has built up.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Cold store Evaporator cleaning

    Ohh Grizzly why do you have to be so much trouble?

    I took the comment from the original post as never needs cleaning. So I might have read more into than I thought on the first pass. My bad.

    We agree now.

    And yes, anything more than every five years or so is excessive (unless the atmosphere is filthy).
    If all else fails, ask for help.


  9. #9
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Cold store Evaporator cleaning

    surely the coil / drip pan etc requires cleaning yearly with a suitable solution for the following possible reasons -

    legionella
    listeria
    salmonella
    any other growths!!

    the potenial risk is low, but should be taken into consideration?

    Billy Ray

  10. #10
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Cold store Evaporator cleaning

    Thanks All
    Your replies are interesting but these are very large coldstores operating with fork lift trucks (gas & electric) the evaporators are very dirty at present with pull down temperatures taking a lot longer.
    A dirty evaporator will have its heat transfer coefficient reduced. Can this be measured? Before critical level is reached where air flow reduction is noted.
    An annual cleaning that I have suggested is for an assesment thereby a preventitive maintenance and planned maintenance can reduce the reactive maintenance.
    With an innitial annual inspection your suggested five year shedule can be factored as an achievable goal for the client.

  11. #11
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Cold store Evaporator cleaning

    Billy Ray
    Your response is in the track that I am taking as the majority of product is fruit. There is a noted increase in fruit degradation due to mould/spores etc
    The trays are suffering with blocked drain lines due to growth build up.

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Cold store Evaporator cleaning

    Quote Originally Posted by hookster
    ...the evaporators are very dirty at present with pull down temperatures taking a lot longer.
    Have you investigated other possible factors? Or, are you attributing the capacity problem only to the dirty coils?

    One other area to look at is the fans themselves. If a centrifugal fan is being used I have seen the blades of the fan wheel accumulate a lot of dirt also. This drastically reduces the discharge air volume of the fans, and hence the coil capacity decreases.

    If this is an old cold store the coils may be flooded ammonia and oil has accumulated in the coils.

    If the coils are DX the TXV's may have been closed down to reduce liquid carryover caused by worn valve pins and carriers.

    More thing scan be discussed if the system is one of the *****s.

    There are a lot of issues, but lack of pull down capacity is a big topic which I'm not sure we could attribute it all to dirty coils.
    Last edited by US Iceman; 11-05-2008 at 06:14 PM. Reason: edited quote
    If all else fails, ask for help.


  13. #13
    kevbrowning's Avatar
    kevbrowning Guest

    Smile Re: Cold store Evaporator cleaning

    Hi guys,

    Our evaporators coils were clogged up and we got a company in called (JMP Industrial Cleaning Services)
    to clean our units, they specialize in cleaning coldstores and evaporators,afterwards our evaporators worked alot better and we saved about 10% on our yearly electricity costs, so we now get them cleaned on a yearly basis as a precaution. There are not many companies around that specialize in this type of cleaning but if you need your equipment cleaning then i couldnt speak more highly of them.


    jmpcleaningservices . co . uk

Similar Threads

  1. cold store doors
    By smpsmp45 in forum NH3
    Replies: 6
    Last Post: 10-09-2008, 03:41 PM
  2. Replies: 15
    Last Post: 17-06-2008, 11:07 PM
  3. Cold Store calc
    By borley in forum Tools and Calculators
    Replies: 2
    Last Post: 19-10-2007, 08:23 PM
  4. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Replies: 12
    Last Post: 17-11-2005, 12:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •