17-06-2008, 09:57 PM #1
Re: fault on a daikin Roundflow
When you go into the settings on the controller it eaithe says 0-01 or 0-02 meaning its either a split or a twin. This had the setting of 0-02 meaning the controller recognised that the sytem was a twin.
Yes that's right, to the master first then through to the slave unit. The controller is wired into P1 P2 in the master unit.
They should configure themselves manually i was told when the power supply is turned off the turned back on. When i first went to it today and changed the board the setting on the controller on setting "21" was 0-01 meaning it was set up as a split not a twin.
Checked for crossed wiring and for any breaks in the cable.The difference between genius and stupidity is that genius has its limits.
Marc