Re: running the oil pump to check oil level
on a centrif the oil cicuit is not 100 % tight some oil will be discharged into the ref circuit with just the pump running so if you have a job where the bas is starting/stopping the chiller alot you may not have enough run time for the oil recovery system to return oil to the sump.