    Question Mitsi split freezing HP pipe



    Hi,
    Right I'm going to poke my head above the trench and see what happens!
    I fitted a SRK40HD about 2-3 years ago. All has worked fine until this week
    When in cooling mode the HP pipe freezes up until the system shuts down. I've took all the covers off the outdoor unit to find the pipe only freezes up after an electrically controlled valve, so I figure that's the problem. It seems to work ok in heating mode.
    There's only a pipe in and a pipe out on this valve, but it has 4 or 5 wires (getting dark outside)
    So to the questions...
    Is this the electronic expansion valve?
    Is there a way to test it?
    Can it be freed off or fixed without replacing it?
    If not who could fit me a new one, I don't want to be brazing that together!
    Cheers,
    Gavin



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Mitsi split freezing HP pipe

    HP pipe??

    Are we talking about the smaller of the 2 pipes to the indoor unit?

    Yes, that valve is most likely the expansion valve but it's not a common failure point.

    Have you checked the airflows and subcooling/superheat?

  3. #3
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: Mitsi split freezing HP pipe

    Quote Originally Posted by Bat View Post
    Hi,
    Right I'm going to poke my head above the trench and see what happens!
    I fitted a SRK40HD about 2-3 years ago. All has worked fine until this week
    When in cooling mode the HP pipe freezes up until the system shuts down. I've took all the covers off the outdoor unit to find the pipe only freezes up after an electrically controlled valve, so I figure that's the problem. It seems to work ok in heating mode.
    There's only a pipe in and a pipe out on this valve, but it has 4 or 5 wires (getting dark outside)
    So to the questions...
    Is this the electronic expansion valve?
    Is there a way to test it?
    Can it be freed off or fixed without replacing it?
    If not who could fit me a new one, I don't want to be brazing that together!
    Cheers,
    Gavin

    i think misti call it an LEV,as the viking said abit more info and we will try to help
    Paul


    "KEEP IT COOL"

  4. #4
    Bat's Avatar
    Bat Guest

    Re: Mitsi split freezing HP pipe

    Hi,
    Yes small pipe sorry :O
    It's only got a port on the suction side, so I can't
    Air flow fine no piles of leaves or blocked filters....
    Cheers,
    Gavin

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Mitsi split freezing HP pipe

    Recover refrigerant and measure his weight. If weight is correct, check sensors at outdoor unit.

    Also, check this troubleshooting of LEV after you checked above mentioned.
    http://www.mediafire.com/?r7jrjxc5zzz
    Last edited by nike123; 08-05-2008 at 07:33 AM.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Mitsi split freezing HP pipe

    Based on the information so far, this seems to be a split unit fitted by a non refrig engineer.

    Best guess is that it has slowly lost part of it's original charge (factory weight?) over the past 2 years and is now short of gas, hence the frosting after the EEV (LEV)

    Nike's recommendation to recover and weigh the charge is spot on and the first place to look.

    But, I doubt that our poster has the equipment to do this

  7. #7
    Bat's Avatar
    Bat Guest

    Unhappy Re: Mitsi split freezing HP pipe

    Quote Originally Posted by frank View Post
    Based on the information so far, this seems to be a split unit fitted by a non refrig engineer.

    Best guess is that it has slowly lost part of it's original charge (factory weight?) over the past 2 years and is now short of gas, hence the frosting after the EEV (LEV)

    Nike's recommendation to recover and weigh the charge is spot on and the first place to look.

    But, I doubt that our poster has the equipment to do this
    Hi,
    I spoke to a friend (commercial engineer, huge stuff) and he said the same.
    I guess I'll have to find an empty recovery cylinder as mine has 134 in at the moment having been empty for months
    I'm used to systems with TXV bolted on the evap coil :O
    Cheers,
    Gavin

  8. #8
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Mitsi split freezing HP pipe

    Agree, check charge first, however I've had three faulty LEV's on Misti Elec's in the last 6 months albiet VRF units so it can't be ruled out.

  9. #9
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    251
    Rep Power
    17

    Re: Mitsi split freezing HP pipe

    Quote Originally Posted by Bat View Post
    Hi,
    Right I'm going to poke my head above the trench and see what happens!
    I fitted a SRK40HD about 2-3 years ago. All has worked fine until this week
    When in cooling mode the HP pipe freezes up until the system shuts down. I've took all the covers off the outdoor unit to find the pipe only freezes up after an electrically controlled valve, so I figure that's the problem. It seems to work ok in heating mode.
    There's only a pipe in and a pipe out on this valve, but it has 4 or 5 wires (getting dark outside)
    So to the questions...
    Is this the electronic expansion valve?
    Is there a way to test it?
    Can it be freed off or fixed without replacing it?
    If not who could fit me a new one, I don't want to be brazing that together!
    Cheers,
    Gavin
    The SRK40 HD fixed speed model was not fitted with HP control for all year round cooling. Min ambient for cooling was approx. 21c. What's the application? Many people who fitted these systems in comms rooms got caught out. I believe the latest models do now have HP control as standard (still only £248 nett trade for 4kW split). Cheap is sometimes not always cheerfull.
    If in doubt read the instructions. If still in doubt follow them.

Similar Threads

  1. pipe freezing just outside the compressor
    By guestingmale in forum Domestic
    Replies: 71
    Last Post: 24-08-2008, 07:57 PM
  2. Split System max pipe run length?
    By fridge doctor in forum Air Conditioning
    Replies: 4
    Last Post: 18-08-2007, 01:14 AM
  3. extra length v pipe size v additional charge
    By misterfixit in forum Air Conditioning
    Replies: 18
    Last Post: 03-01-2007, 08:57 PM
  4. Split type wall mounting Air Conditioning system
    By stevews in forum Air Conditioning
    Replies: 23
    Last Post: 11-07-2005, 09:55 AM
  5. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •