07-05-2008, 11:59 PM #1
Mitsi split freezing HP pipe
Hi,
Right I'm going to poke my head above the trench and see what happens!
I fitted a SRK40HD about 2-3 years ago. All has worked fine until this week
When in cooling mode the HP pipe freezes up until the system shuts down. I've took all the covers off the outdoor unit to find the pipe only freezes up after an electrically controlled valve, so I figure that's the problem. It seems to work ok in heating mode.
There's only a pipe in and a pipe out on this valve, but it has 4 or 5 wires (getting dark outside)
So to the questions...
Is this the electronic expansion valve?
Is there a way to test it?
Can it be freed off or fixed without replacing it?
If not who could fit me a new one, I don't want to be brazing that together!
Cheers,
Gavin
-
08-05-2008, 12:31 AM #2
Re: Mitsi split freezing HP pipe
HP pipe??
Are we talking about the smaller of the 2 pipes to the indoor unit?
Yes, that valve is most likely the expansion valve but it's not a common failure point.
Have you checked the airflows and subcooling/superheat?
-
08-05-2008, 12:34 AM #3
-
08-05-2008, 12:36 AM #4
Re: Mitsi split freezing HP pipe
Hi,
Yes small pipe sorry :O
It's only got a port on the suction side, so I can't
Air flow fine no piles of leaves or blocked filters....
Cheers,
Gavin
-
08-05-2008, 07:20 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: Mitsi split freezing HP pipe
Recover refrigerant and measure his weight. If weight is correct, check sensors at outdoor unit.
Also, check this troubleshooting of LEV after you checked above mentioned.
http://www.mediafire.com/?r7jrjxc5zzzLast edited by nike123; 08-05-2008 at 07:33 AM.
-
08-05-2008, 09:44 PM #6
Re: Mitsi split freezing HP pipe
Based on the information so far, this seems to be a split unit fitted by a non refrig engineer.
Best guess is that it has slowly lost part of it's original charge (factory weight?) over the past 2 years and is now short of gas, hence the frosting after the EEV (LEV)
Nike's recommendation to recover and weigh the charge is spot on and the first place to look.
But, I doubt that our poster has the equipment to do this
-
09-05-2008, 07:36 PM #7
Re: Mitsi split freezing HP pipe
-
12-05-2008, 08:21 PM #8
Re: Mitsi split freezing HP pipe
Agree, check charge first, however I've had three faulty LEV's on Misti Elec's in the last 6 months albiet VRF units so it can't be ruled out.
-
13-05-2008, 12:01 AM #9
Re: Mitsi split freezing HP pipe
The SRK40 HD fixed speed model was not fitted with HP control for all year round cooling. Min ambient for cooling was approx. 21c. What's the application? Many people who fitted these systems in comms rooms got caught out. I believe the latest models do now have HP control as standard (still only £248 nett trade for 4kW split). Cheap is sometimes not always cheerfull.
If in doubt read the instructions. If still in doubt follow them.
Similar Threads
-
pipe freezing just outside the compressor
By guestingmale in forum DomesticReplies: 71Last Post: 24-08-2008, 07:57 PM -
Split System max pipe run length?
By fridge doctor in forum Air ConditioningReplies: 4Last Post: 18-08-2007, 01:14 AM -
extra length v pipe size v additional charge
By misterfixit in forum Air ConditioningReplies: 18Last Post: 03-01-2007, 08:57 PM -
Split type wall mounting Air Conditioning system
By stevews in forum Air ConditioningReplies: 23Last Post: 11-07-2005, 09:55 AM -
Pipe sizes
By benncool in forum Chit Chat & Service StoriesReplies: 10Last Post: 08-07-2003, 10:58 PM