    Heat Pump Issues!!!



    Hello everybody

    I'm having an issue with a Climate Master Heat pump on a new installation. The unit runs in cooling for about 20 mins then the system pumps down with out hitting setpoint, a few times it ran for about 2hrs or more. The system runs fine in heating. Could it be crap in the reversing valve??? I've recovered the gas and evacuated the system down to 250 microns, scaled in fresh R-410a and its still acting the same.

    Please help. Climate master is not helping at all!!!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Heat Pump Issues!!!

    You say the unit 'pumps down', is this a gradual process or does it happen quite quickly?

    Is there a non-return valve that is sticking in the cooling mode that isn't letting the gas by?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    Honolulu Hawaii
    Age
    42
    Posts
    5
    Rep Power
    0

    Re: Heat Pump Issues!!!

    It pumps down really quick like in a matter of seconds. And the only valve in the refrigeration circuit is the txv and the 3 way valve which I have going to straight power, bypassing the relay just to make sure there wasen't a problem with the printed circuit board (Which I've also had problems with), or a power issue.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Heat Pump Issues!!!

    There will probably be two non-return valves in the system, one at the evaporator and one at the condenser.

    It is possible that one of them is sticking and blocking the flow.

    They may only look like a larger section of pipe not necessarily a 'valve'.

    edit: Sorry Brian, forgot to ask, which model is it?
    Also, having had a quick look at the data on the Climate Master website it seems that they use a reversible expansion valve so my comments could be rubbish.....
    Last edited by Brian_UK; 09-05-2008 at 12:21 AM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Heat Pump Issues!!!

    Quote Originally Posted by Brian_UK View Post
    There will probably be two non-return valves in the system, one at the evaporator and one at the condenser.

    It is possible that one of them is sticking and blocking the flow.

    They may only look like a larger section of pipe not necessarily a 'valve'.

    edit: Sorry Brian, forgot to ask, which model is it?
    Also, having had a quick look at the data on the Climate Master website it seems that they use a reversible expansion valve so my comments could be rubbish.....

    I agree with Brian..

    If it has a TEV it will have one way valves around it so the refrigerant can flow in the other direction.
    If it has a valve befor the evap what restricts the pressure to the cond on heat mode because if it is another valve that will have one way valve as well.
    The only othe option is a capilary but again that requires a bypass dependant on flow direction.

    Thanks taz.

  6. #6
    Join Date
    Oct 2007
    Location
    Honolulu Hawaii
    Age
    42
    Posts
    5
    Rep Power
    0

    Re: Heat Pump Issues!!!

    Quote Originally Posted by Brian_UK View Post
    There will probably be two non-return valves in the system, one at the evaporator and one at the condenser.

    It is possible that one of them is sticking and blocking the flow.

    They may only look like a larger section of pipe not necessarily a 'valve'.

    edit: Sorry Brian, forgot to ask, which model is it?
    Also, having had a quick look at the data on the Climate Master website it seems that they use a reversible expansion valve so my comments could be rubbish.....

    The model # is TRM24 it's part of the Tranquility series. And yes the unit has a reversible expansion valve. Thats y I'm puzzled on why it runs in Heating perfectly fine but in cooling it pumps down. So far with these units I'm not impressed at all. We installed 527 of these units and we had to change all of the evaporator thermistors because all the units were going out on low air coil temp, the factory said it was a bad batch. A several LOCKed compressors, a few boards, a whole lot of factory leaks in the water and the refrigeration lines. It's been really frustrating.

    I really appreciate the help and info. Thanks

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Heat Pump Issues!!!

    First check Reversing valve by measuring temperature difference at his pipes and then check filter-dryer also with temperature difference test. If OK, than could be reversible TXV.

  8. #8
    Join Date
    Sep 2010
    Location
    South Africa
    Posts
    7
    Rep Power
    0

    Re: Heat Pump Issues!!!

    how long have you had the heat pump for?

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat Pump Issues!!!

    Quote Originally Posted by Fire Fly View Post
    how long have you had the heat pump for?
    At least 2 years 4 months, by now.

    LOL... old post.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 08:49 PM
  2. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Will this heat pump work?
    By goodguy in forum Heat Pumps
    Replies: 7
    Last Post: 08-03-2008, 05:14 PM
  5. Domestic VRF heat pump?
    By electronicsuk in forum Heat Pumps
    Replies: 8
    Last Post: 30-10-2007, 08:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •