    designing an evaporator qith thermal load 30 kWatt
    to cool air from 45 to 21 °c
    with operating temperature of 10 °c inside tubes
    temperature,pressure of refrigerant at outlet inlet is unknown

    i need to calculate mass flow rate as following:

    flow rate = thermal load /
    enthalpy out - enthalpy in


    what enthalpy values should i use

    those of refrigerant ?
    or of (water) saturated liquid,vapor ?

    difference in enthalpy for refrigerant is much lower than those of water and it confuses me
    help plz
    Last edited by 7ramy; 06-05-2008 at 03:22 AM.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: One Student Question

    For the refrigerant enthalpy difference you need to know the condensing temperature of the refrigerant being used. Let's say the condensing temperature is 35°C. You provided the evaporator temperature of +10°C.


    Also, to keep this simple we will assume there is no superheat being done in the evaporator.

    So, you need to find the liquid enthalpy at 35°C. This is referred to as hf, or the liquid enthalpy.

    Next you need to find the saturated vapor enthalpy at +10°C. This is referred to hg, or vapor enthalpy.

    thermal load / (hg-hf) = mass flow

    If the vapor is superheated in the evaporator then the value for hg is based on the vapor enthalpy at the superheated condition. Use the evaporating pressure @ +10°C (in the superheat tables) and look up the vapor enthalpy at that pressure and actual vapor temperature.

    The actual vapor temperature is the saturated temperature plus the degrees of superheated created in the evaporator.
    If all else fails, ask for help.


Similar Threads

  1. Heat Transfer Exam Question
    By alexdouglas1969 in forum Fundamentals
    Replies: 10
    Last Post: 13-12-2008, 05:19 PM
  2. Refriferation cycle question
    By ozmecheng in forum Fundamentals
    Replies: 32
    Last Post: 26-03-2008, 11:38 PM
  3. Hitachi RAC25NH5 question
    By Yonas in forum Heat Pumps
    Replies: 11
    Last Post: 30-01-2008, 11:53 AM
  4. Student question
    By WebRam in forum Technical Discussions
    Replies: 36
    Last Post: 13-02-2007, 05:19 AM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 04:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •