    hi friends..... i need to know what are the stages that refrigerant undergoes when it passes through the condenser....



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: hi i am new to this site.....

    The obvious: from gas to liquid!

  3. #3
    Join Date
    Apr 2008
    Location
    philippines
    Posts
    95
    Rep Power
    17

    Re: hi i am new to this site.....

    Quote Originally Posted by kumar9172 View Post
    hi friends..... i need to know what are the stages that refrigerant undergoes when it passes through the condenser....
    when refrigerant go out the compressor [discharge line-high side] 1/4 or not exactly 1/4 maybe even less than 1/4 of the condenser the state of the refrigerant there is still gas going to liquid. when the refrigerants pass through out the condeser it is in liquid state. after the condenser it is the [liquid line]
    followed by drier or sigth glass. after the liquid line you will see expansion devices such as capillary or thermostatic expansion valves "TXV" after expansion devices is the evaporator. in evaporator the state of refrigerant is from small particles liquid to gas. refrigerants evaporates here depends on your heat load. after evaporator is the suction accumulator and finally [low side-suction line] back to compressor.

    Refrigeration Cycle Welcome Aboard.....

    _____________________________________________
    brian
    SAMSUNG Tech. Support

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hi i am new to this site.....

    1) Desuperheating - gas looses temperature (sensible heat)

    2) Phase change - from gas to liquid (latent heat)

    3) Subcooling - liquid cooled from higher temperature to lower temperature (sensible heat). Note: some condenser may not provide subcooling, but others may.
    Last edited by US Iceman; 23-05-2008 at 09:06 PM. Reason: fix spelling
    If all else fails, ask for help.


  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hi i am new to this site.....

    This is what I got as answer to similar question




  6. #6
    Join Date
    May 2008
    Location
    California
    Age
    69
    Posts
    11
    Rep Power
    0

    Re: hi i am new to this site.....

    Welcome Kumar,
    After the refrigerant is compressed it's superheated vapor, as it passes through the condenser, it becomes sub cooled liquid and on to the metering device which will change it back to a vapor (low pressure), where it will be super-heated vapor to return to the compressor.

  7. #7
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: hi i am new to this site.....

    Well let us put it in a mathematical physical way:

    1) the refrigerant will loose enery to go to it's condesing tempreture Q= m.c.deltaT (sensible)
    2) the refrigerant will condense by loosing energy at constant tempreture Q=m.L (latent)
    3) the refrigerant will be subcooled by loose of energy and tempreture Q=m.c.deltaT (sensible)

    That's in a simple way , the calculation is a lot more complicated due to the friction losses in the tubes and bendings which directly affects "c" so an integral based calculations should be made to get precise results.

    Respects and regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

Similar Threads

  1. Drier then site glass why?
    By Andy T in forum Commercial
    Replies: 7
    Last Post: 15-09-2006, 09:59 PM
  2. Mitsubishi A/C Web Site
    By garyjh24 in forum Technical Speculations
    Replies: 2
    Last Post: 11-07-2006, 09:35 PM
  3. white goods web site
    By ksvinod in forum Computers & the Internet
    Replies: 4
    Last Post: 06-09-2005, 08:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •