    Liquid refrigerant and bubles in sightglass



    Hello everybody,
    Today I faced a problem. I would like to give some information…
    There is an aircooled unit (air cooled condenser and air cooled evaporator). In this unit We charged refrigerant R407C and run it. We saw that condensing temperature is apr. "45.7C ", evaporating temp is apr." -2C" and ambient temperature is apr. "30C"… When we look in sightglass ( sightglass is located before expansion valve) we saw liquid refrigerant and bubles... I couldn't say "undercharge problem - absence of refrigerant" because condensing temperature is ok not low…, but evaporating temp is low I thing…

    If the refrigerant is overcharge condensing and evaporating temperatures will be high…I thing this is not also overcharge problem…
    Can it be an expansion valf problem?… (TEV)

    What do you think?

    Thanks for your helps…
    Best Regards…



  2. #2
    Join Date
    Jan 2002
    Location
    turkey
    Age
    54
    Posts
    22
    Rep Power
    0
    Is this problem related with wrong expansion valve adjustment?...
    Regards

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    This is not enough information.