    Temp. Rise at duct outlet



    Hi,

    While performing a test in a low temp air chiller, the outlet temp from the coil was -25F.

    At the fan inlet (Plug Fan), which is 10" from the coil, the temp is 6F.

    At the outlet of the 10" dia duct, which is only 6" long, temp is again 6F.

    Air qty -- 500 CFM.

    Can someone suggest, where and what we are doing wrong.

    Checked the temp display and the sensor and all found OK.

    Tried testing with different tester and same results, when sensor is at the coil outlet, temp is -25F and at the fan inlet temp is 6F and same at the fan outlet.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Temp. Rise at duct outlet

    What is the air inlet temperature ?

    Is that -25°F an air temperature or a pipe temperature?

    What size is the coil in relation to the duct size?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Temp. Rise at duct outlet

    Is it possible that air somehow bypassing coil? Could you describe little more that evaporator-fan-duct setup?

  4. #4
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Temp. Rise at duct outlet

    Is the fan running backwards?
    Last edited by wambat; 05-05-2008 at 01:21 AM.

  5. #5
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Temp. Rise at duct outlet

    Air Inlet Temp (Coil Inlet) is 70F.

    Air coming out of the coil is -30F.

    Air outlet at fan is 6F.

    Coil dimension are 12" X 15".

    Fan -- 10"dia centrifugal, direct coupled- 0.16 KW.

    Duct outlet -- 10".

    CFM -- 400-500.

    Fan is not running backward.

    The air temp is measured at coil outlet, between coil and fan inlet venturi ring.

    Did smoke test in the coil/fan chamber and found no leaks.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Temp. Rise at duct outlet

    Can you confirm the air flow rate is actually 400-500cfm?

    What is the fan motor temperature as this is in the airflow it will affect the air temperature.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Temp. Rise at duct outlet

    I checked the air flow rate and is actually 450cfm.

    Fan is enclosed and motor temp cant be checked.

  8. #8
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Temp. Rise at duct outlet

    This should realy not be possible at all. The only solution I see is air by-passing the coil. Are you sure of your -30F reading? Can you move the sensor to different locations, at the very end or side of the coil, not in the middle. Where exactly do the temp rise occur?

  9. #9
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Temp. Rise at duct outlet

    I am getting -30F after 4" of the coil outlet.

    Temp rise occours at the fan outlet.

  10. #10
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Temp. Rise at duct outlet

    Ok, is the temperature -30F at the very fan inlet and 6F at the outlet? If so, this indicates the fan is responsible for the temp rise. I suppose absolutely no outside air is drawn into the fan inlet. If the air flow is very low, then it will be a substantly temp rise over the fan. You have 30-35F temp rise over the fan. 160W ejected into an air flow of roughly 21 CFM give a temp rise of roughly 35F. Are you absolutely sure of your air flow? Is the fan consuming substantly more power than it should be? You should maybe measure the amperage of the fan. How is the ducts insulated? Porly insulation also adds to the increase of temp.

  11. #11
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Temp. Rise at duct outlet

    Thanks SteinarN,

    As U mentioned about the poor insulation, I think that could be the reason as I see lots of condensation on ONE side of the Insulated panels.

    I'll double check this again.

  12. #12
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Temp. Rise at duct outlet

    SteinerN is correct,this is not possible.In your old money at the flow rates and temperatures described the coil is removing 54,000btus/hr ( 15.83Kw ) so if the fan is only rated at 160watt it cannot be responsible for the heat gain occurring at the fan outlet.The heat gain you describe equates to 36% of what has been removed so that is 19,444btus/hr ( 5.7Kw ) Also unless the coil is minimum 6 row I fail to see how the coil size given can provide the cooling effect anyway so suggest you provide some more detail on the system ie refrigerant,application,compressor details,other components fitted etc.How about a jpeg even.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Temp. Rise at duct outlet

    Hi, jwasir!
    You say "low temperature air chiller"! Does that evaporator coil have defrost heaters. If you have defrost heater, is it possible that heater is on?

  14. #14
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Temp. Rise at duct outlet

    The Evap is 10 rows deep and it has HG defrosting...

    I still beleive the temp rise is due to poor insulation.

    Thanks everyone!!!

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. opens on rise of outlet
    By subzero*psia in forum Commercial
    Replies: 24
    Last Post: 01-03-2008, 10:46 AM
  4. Freezer Room Heat Rise in Temp
    By Kenny Pollin in forum Fundamentals
    Replies: 2
    Last Post: 08-09-2007, 01:00 PM
  5. Endless Freezer as Endless Cooler (10 door)
    By herefishy in forum Commercial
    Replies: 95
    Last Post: 17-04-2002, 12:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •