    York Liquid Chiller problems.



    I have been working on a York Liquid Chiller M#YCAZ33BA3-46PA S#RKEM6953AA. I have a system fault of "Motor Current". I have (2) O6Z's reciprocating compressors 6 cylinder type. Both compressors are not original and have been replaced at one time or another. I went to the trouble shooting section of the operations manual and they suggest (3) different things will cause this alarm. Bad relay output board, bad motor protection device and faulty high pressure switch. The relay output board was replaced about a year ago. I checked my high pressure switch and is working correctly. I swapped out the motor protection between compressors and still had a system fault on Circuit (2) which disables Circuit 2 compressor. The tests I have done till now are as follows: Performed acid test on Circuit (2) compressor. Megged out the condenser fan motors. Both came back satisfactory. My next step is going to get oil sample to send over to a lab and get analyzed. Any other suggestions would be appreciated.



  2. #2
    Join Date
    Mar 2002
    Location
    northants uk
    Posts
    5
    Rep Power
    0

    Re: York Liquid Chiller problems.

    hi
    check that there is not two hp switches on unit also check current relay which monitors compressor amps if it is reading too high or too low it will shut down unit hope this helps
    nick

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York Liquid Chiller problems.

    Quote Originally Posted by kanodogg View Post
    I have been working on a York Liquid Chiller M#YCAZ33BA3-46PA S#RKEM6953AA. I have a system fault of "Motor Current". I have (2) O6Z's reciprocating compressors 6 cylinder type. Both compressors are not original and have been replaced at one time or another. I went to the trouble shooting section of the operations manual and they suggest (3) different things will cause this alarm. Bad relay output board, bad motor protection device and faulty high pressure switch. The relay output board was replaced about a year ago. I checked my high pressure switch and is working correctly. I swapped out the motor protection between compressors and still had a system fault on Circuit (2) which disables Circuit 2 compressor. The tests I have done till now are as follows: Performed acid test on Circuit (2) compressor. Megged out the condenser fan motors. Both came back satisfactory. My next step is going to get oil sample to send over to a lab and get analyzed. Any other suggestions would be appreciated.
    Hi can you please confirm that the model code you have posted is correct??
    Cheers Grizzly

  4. #4
    kanodogg's Avatar
    kanodogg Guest

    Re: York Liquid Chiller problems.

    Yes,the model and serial number information is correct. This is a very old Chiller.

  5. #5
    johntheboy's Avatar
    johntheboy Guest

    Re: York Liquid Chiller problems.

    Try checking the motor thermistors. If they are open circuit then the compressor won't run. If the machine has an opto-isolator board then there should be 2 red LEDs in the top right hand corner that should be on if the thermistors are ok.

Similar Threads

  1. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Replies: 7
    Last Post: 13-08-2010, 08:12 PM
  2. chiller problems
    By iceman6869 in forum Technical Discussions
    Replies: 8
    Last Post: 19-11-2009, 07:47 AM
  3. problems with york yaa c chiller
    By paulwild in forum Commercial
    Replies: 4
    Last Post: 21-08-2007, 08:20 PM
  4. Oversized Liquid Recievers?? Problems??
    By nickjh in forum Fundamentals
    Replies: 12
    Last Post: 12-06-2007, 07:54 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •