Results 1 to 8 of 8
Thread: Hubbard cellar cooler
03-05-2008, 09:13 AM #1
Hi guys,
This is probably an easy one for most of you but my refrigeration work is limited!This cellar cooler will not cool It appears to have pumped itself down. It's out on L.P and has liquid in the receiver. It seems to me to have a restriction on the liquid line. The solenoid is energised and lifts ok. Is it the exp valve? Am i going in the right direction?
03-05-2008, 09:48 AM #2
Re: Hubbard cellar cooler
Hi Birchy
Yes it does sound like the Txv.Pour some warm water over the valve to check if you have moisture in it.If the valve clears then you will have to pump down again and replace L/L drier.
If it does not clear with water,strip the valve down as you have a strainer inside the orifice capsule which may be blocked.
If this does not help,post back.If it ain't broke, it doesn't have enough features yet.
Damo
03-05-2008, 09:53 AM #3
Also,you might have a blockage in the liquid line filter drier which is stopping the refrigerant getting to the Txv.
Damo
03-05-2008, 10:00 AM #4
Thanks Chunk, i'll let you know the outcome.
03-05-2008, 11:21 AM #5
03-05-2008, 01:57 PM #6
It can be many things:
-A broken TEV capilar tube.
-A blocked drier.
-Blocked TEV filter in the orifice.
-Lack of refrigerant-a sign of a leak!
And so on.......
Chemi
06-05-2008, 10:05 PM #7
Thanks all !
The gauze was blocked in the orifice in the txv.
06-05-2008, 11:46 PM #8
There you go..... thanks for the update - now the important thing ...
Is the beer cold ?Brian - Newton Abbot, Devon, UK
NRS BeerMaster cellar cooler
By madfriday in forum CommercialReplies: 13Last Post: 22-06-2009, 09:24 PM -
Searle cellar cooler
By cold as ice in forum Technical DiscussionsReplies: 19Last Post: 13-01-2009, 01:09 PM -
cellar cooler fault.
By fireblade in forum CommercialReplies: 12Last Post: 11-07-2007, 11:33 AM -
Cellar cooler in the 'Vic
By shanes696 in forum CommercialReplies: 6Last Post: 19-12-2005, 10:43 PM -
Searle cellar cooler control problem
By iceman007 in forum ElectricalReplies: 6Last Post: 06-07-2004, 08:57 PM