    Oversizing EXV electronic expansion valve



    Hello everybody,

    In our cooling units we are using 20 tons electronic expansion valve, but i want to use 30tons expansion valve instead of 20 tons in our system ( reason stock problem) . We are using these units not only for summer application but also for proses cooling (winter and summer).

    What kind of problems does it cause if we use "oversizing step motor electronic expansion valves (EXVs)" ?

    Thanks for your comments…

    Regards



  2. #2
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23

    Question

    Aygul

    I would imagine that restricting refrigerant flow will be a major problem due to the larger oriface size in the 30ton eev

  3. #3
    Join Date
    Jul 2003
    Location
    ksa
    Age
    58
    Posts
    22
    Rep Power
    0
    Hi Aygul,

    EEV or EXV could be oversized to a certain extent but unfortunately I don't know the figures.

    Malfunctions on oversize EEV's could be some delayed responses.

    I mean wider gate takes more time to close.

    However, if the controller is program properly with regards to the superheat, minimun start-up opening, proportional band and integral time then no much hassle to expect.

    More importantly is to calibrate the EEV as per manufacturers instructions and always use a compatible controller (same manufacturer matching).

  4. #4
    Join Date
    Jan 2002
    Location
    turkey
    Age
    54
    Posts
    22
    Rep Power
    0
    In our system we are controling exv acording to the superheat . According to that i thought we can use 30tons exv instead of 20tons.

    Could you please tell me Is it correct or not?
    Regards

  5. #5
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    aygul, in general, one should not run into any problems using a 30 ton step motor EEV on a 20 ton load. This assumes your controller is effective in controlling the EEV for the type of equipment it is applied.
    Prof Sporlan

  6. #6
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    66
    Posts
    78
    Rep Power
    21
    it should be no problem at all, just be sure it is closed when needed. the steps will have to be a little faster as flooding could be a problem, never saw it however as control even in freezing is good. If your car is able to drive 30 miles it also can run 20 miles without problems you will see it will hunt a little more. but hey it is driving and or cooling.

Similar Threads

  1. electronic expansion valve issue
    By Lc_shi in forum Fundamentals
    Replies: 17
    Last Post: 12-06-2009, 11:30 AM
  2. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  3. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  4. Replies: 2
    Last Post: 07-09-2005, 03:07 PM
  5. pressure drop between expansion valve and distributor
    By aygul in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2004, 09:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •