    Question pressure control settings



    In pump down refrigeration systems what cut-in/cut-out settings on the pressure control are ideal or correct? I'm asking for both medium and low temp applications. Thanks.



  2. #2
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: pressure control settings

    Cut out:
    Low enough that the compressor don't stop under normal operating conditions. Lets say SST -20*C on a system operating normally at -10*C. -40*C on a system operating at -30*C.

    Cut in:
    Slightly lower than the normal room temperature. Lets say SST -25*C on a -20*C freezer and -5*C on a coold room system.

    Spesific conditions on each system may make it necessarry to deviate from these values, but as a starting point they should be ok.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: pressure control settings

    When pumping down or if the thing lost its gas you do not want it to go into a vacum so set the cutout at just above zero about 0.2b or 2-3psi in old money.

    For cut in you want as wide a differential as possible without the temp being affected and that will depend on the refrigerant and the opperating temp.


    Cheers taz.

  4. #4
    Join Date
    May 2008
    Location
    Hawaii
    Posts
    5
    Rep Power
    0

    Re: pressure control settings

    [quote=SteinarN;104024]Cut out:
    Low enough that the compressor don't stop under normal operating conditions. Lets say SST -20*C on a system operating normally at -10*C. -40*C on a system operating at -30*C.

    Cut in:
    Slightly lower than the normal room temperature. Lets say SST -25*C on a -20*C freezer and -5*C on a coold room system.

    Spesific conditions on each system may make it necessarry to deviate from these values, but as a starting point they should be ok.[/quote]


    So by room temperature, you mean box/space temperature? Does the same go for multiple evap/cooler applications? In this case is it possible to set cut in pressure slightly above evap coil freezing temp (converted to pressure) to allow defrost without affecting temp too much in any box connected to this system. Thus the elimination of any mechanical defrost timers?

  5. #5
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: pressure control settings

    Quote Originally Posted by jcool808 View Post
    So by room temperature, you mean box/space temperature?
    Yes, box temperature.
    Quote Originally Posted by jcool808 View Post
    Does the same go for multiple evap/cooler applications?
    Yes, set the cut in slightly lower than the SST for the lowest temp room or case. But be aware of short cycling protection if it is not sufficient capasity regulation on the compressor(s).

    Quote Originally Posted by jcool808 View Post
    In this case is it possible to set cut in pressure slightly above evap coil freezing temp (converted to pressure) to allow defrost without affecting temp too much in any box connected to this system. Thus the elimination of any mechanical defrost timers?
    This solution is new to me. It seems to be a rudimentary defrost system. I will not advice it.
    Last edited by SteinarN; 03-05-2008 at 03:59 AM.

  6. #6
    Join Date
    Jul 2006
    Location
    MODESTO,CA USA
    Age
    67
    Posts
    7
    Rep Power
    0

    Re: pressure control settings

    Ok I am in the USA we are in Farenhight and PSIG not kilo pascals, CAn any help with correct temp/pressure chart for r414b hotshot and is it close for off cycle air cooled defrost? as is R 12

    Please no slamming to us here in CAlifornia From the saddle Bill

  7. #7
    mojica2369's Avatar
    mojica2369 Guest

    Re: pressure control settings

    Quote Originally Posted by jcool808 View Post
    In pump down refrigeration systems what cut-in/cut-out settings on the pressure control are ideal or correct? I'm asking for both medium and low temp applications. Thanks.
    i need to set my control settings

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: pressure control settings

    Quote Originally Posted by mojica2369 View Post
    i need to set my control settings
    What is usage and what refrigerant?

  9. #9
    acdc's Avatar
    acdc Guest

    Re: pressure control settings

    im knew to all this stuff just completed my second fridge year and wondered about stuff like how would u know what to set pressure switches at like low and high side there must be some sort of rule of thumb?

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: pressure control settings

    Quote Originally Posted by acdc View Post
    im knew to all this stuff just completed my second fridge year and wondered about stuff like how would u know what to set pressure switches at like low and high side there must be some sort of rule of thumb?
    High side would be the safety setting that you require for your particular system. You are protecting the compressor and the weakest part of the system.

    Low side it all depends what you are using the LP switch for, safety, temperature, control, pump down.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Mar 2009
    Location
    NZ
    Age
    54
    Posts
    29
    Rep Power
    0

    Re: pressure control settings

    on the high side the hp switch must stop the compressor before the relief valve blows

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •