Thread: One question
-
01-05-2008, 10:37 AM #1
One question
For TXV ;If ı selected orifice bigger than must be,What kind of problems I experience?
-
01-05-2008, 01:31 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: One question
You experience valve hunting!
http://www.ra.danfoss.com/TechnicalI...chapter_01.pdfLast edited by nike123; 01-05-2008 at 01:41 PM.
-
02-05-2008, 08:55 AM #3
Re: One question
Too small SH, compressor will suck partially liquid, oil washout,....
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.