    Hitachi utopia fault code 39



    Hey, having real proplems with a hitachi utopia heatpump single phase. Initially the condensing unit had been tapped by a truck and lost its gas, so repaired and regased. but now error code 39 keeps coming up (overcurrent) so checked the amps to the comp which is fine, so is the current transformer. Then thought maybe a blockage in the system or overgased, so reclaimed and blew nitrogen through (no blockage) then tried running the comp (single phase) unpiped and pressure switches over ridden but power is still tripping to the contactor stopping the compressor. everytime i reset on isolator comp runs for about 3 seconds and then this happens. im a little stumped so any links or help would be apprieciated.
    Last edited by n1redrum; 30-04-2008 at 09:38 PM.



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    welcome the RE n1redrum,

    ok so lets get right into it,by power tripping to the contactor do you mean an overload or at the MCB?
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    just the contactor inside the condensing unit that supplies the compressor (CMC ?). Losing the 240v that makes it A1, A2. so it must be some sort of safety switch cutting it out ???

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Hitachi utopia fault code 39

    Hmm...

    You got an Utopia INVERTER??

    If so there will be more to it than a contactor...

    There might be a contactor feeding the inverter or maybe it isn't an inverter unit as stated in your first sentence??

    If you clarify this, I'm sure the advice we will provide you with will become more accurate.

    Cheers

  5. #5
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    S**t, my apologies. its just a run of the mill single phase heatpump, ive been working on an Danfoss inverter aswell today and my heads right up my backside.

  6. #6
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    Quote Originally Posted by n1redrum View Post
    S**t, my apologies. its just a run of the mill single phase heatpump, ive been working on an Danfoss inverter aswell today and my heads right up my backside.
    lol,ok give us the heads up on the split then
    Paul


    "KEEP IT COOL"

  7. #7
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    everything i put in my first thread refers to the heat pump im having problems with.

  8. #8
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    can you tell ive never written on a forum before, i might just start the whole thread again.

  9. #9
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    Quote Originally Posted by n1redrum View Post
    can you tell ive never written on a forum before, i might just start the whole thread again.

    lol dont worry iam sure we can get you though it,ok what i get so far,split gets bashed,repair leaking,pressure test vac charge ect ect,run system faults on comp over curr and is triping MCB
    Paul


    "KEEP IT COOL"

  10. #10
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    no not on mcb, there is always 240v to the unit. The compressor starts but runs for a few seconds and then cuts out. when the compressor has cut out 3 times the error code 39 (overcurrent) comes up

  11. #11
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    got it!

    id start with checking the compressor.if unsure of how to see:

    http://www.refrigeration-engineer.co...essor+windings
    Paul


    "KEEP IT COOL"

  12. #12
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    windings are fine. and the current the compressor is pulling is also fine. if you push the contactor in the compressor runs. but the voltage to hold the contactor in is cutting out, therefore the compressor cuts out

  13. #13
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    sounds like a faulty contactor,have you checked the voltage at the top and bottom of it?
    Paul


    "KEEP IT COOL"

  14. #14
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    i checked so many things i cant remember, im pretty sure its ok. one of the relays on the pcb clicks and then the power supplying the contactor cuts off.

  15. #15
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    Quote Originally Posted by n1redrum View Post
    i checked so many things i cant remember, im pretty sure its ok. one of the relays on the pcb clicks and then the power supplying the contactor cuts off.

    is this during normal op?
    Paul


    "KEEP IT COOL"

  16. #16
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    there is 240V going through the contactor to the compressor when it is made. 240v supplying it but the 240v supplying it is being cut off after a few seconds when a relay on the pcb clicks

  17. #17
    Join Date
    Aug 2006
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    set to cooling on the dip switch

  18. #18
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Hitachi utopia fault code 39

    Quote Originally Posted by n1redrum View Post
    set to cooling on the dip switch

    PM sent with number as suffering with slow net sindrome
    Paul


    "KEEP IT COOL"

  19. #19
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Hitachi utopia fault code 39

    There is an over current relay on hitachi utopias settings are :

    For ras 2 17A
    ras 2.5 20.5A
    ras 3 25A
    ras 3.5/4 32A + 17A (for cold/prolonged sarting)

    You need to measure your peak starting current and if ti doesnt drop to under the relays setting within 2 - 3 secs then you will get fault 39 thereby indicating a charge or compressor fault (or power). The relay maybe faulty but difficult to test properly unless you have the equipment.

    Last edited by frank; 03-05-2008 at 06:05 PM.

  20. #20
    Join Date
    Jan 2008
    Location
    turkey
    Age
    50
    Posts
    23
    Rep Power
    0

    Re: Hitachi utopia fault code 39

    as far as see from the service manual current sensing for comp motor aligning from current coil ct to outdoor unit pcb cn6 socket so i think as an electronics technician there is an operational amplifier measuring that current value so pull out that cn6 socket from pcb thats way u can be sure that this is a pcb fault or not if its again giving that fault code replace or repair that pcb maybe current coil burnt so be measuring wrong value if it is working without ct (current coil) u cant be sure if pcb faulty or not...good luck

Similar Threads

  1. lennox fault code
    By richelli in forum Trouble Shooting
    Replies: 0
    Last Post: 01-02-2008, 09:13 PM
  2. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  3. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  4. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Replies: 3
    Last Post: 31-10-2006, 07:43 PM
  5. Fault Code Sheets...?
    By C_Henderson in forum Air Conditioning
    Replies: 2
    Last Post: 01-08-2006, 05:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •