    Daikin Compressor failure



    We have installed a Daikin RZQ100C7V1B/FAQ100B which has been in for 5 months, we have been told the compressor has failed can anyone tell me what the compressor winding resistances should be?

    I inspected the unit and found that the noise filter board has also blown is this a common problem that if the compressor fails it blows the boards as well?

    If the compressor has failed as well as the boards it would be a cheaper option just to replce the whole outdoor unit labour wise not sure how Daikin would react to that though.

    Regards Mark



  2. #2
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: Daikin Compressor failure

    Hi Mark

    Whats wrong with the comp, seized, broken windings or down to earth. I would expect resistance to be somwhere beetween 1-5 ohm all equal.

    Regards




    PP

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin Compressor failure

    Only 5 months old - under warranty - send it back and get it replaced.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin Compressor failure

    If it's blown the noise filter, then the compressor is most likely down to earth (always been when I seen this).

    It is also likely to have damaged the inverter board...

    [To check if it's down to earth you will need a proper megger, there should be an open circuit between the compressor's terminals and earth]

    [To check the inverter board, disconnect the compressor and bypass the noise filter then start the unit up and measure the output from the inverter. It doesn't matter what voltage you get between the phases and neutral but it should be the same for all 3 phases]
    Last edited by The Viking; 30-04-2008 at 08:25 AM.

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daikin Compressor failure

    The windings are lower than a standard multimeter will measure, typically 300milli ohms, your regular meter will read 1-1.5 ohms. You don't need to worry about that anyway, it's a short to earth that blows up PCBs usually (especially filter boards, that's a big one), not a short between windings. You need to test resistance with a megger, anything above 10Mohms is good, anything around 2Mohms is suspect, anything below that is shorted.
    Don't forget condenser fans, they can short and blow filter boards too. If they are DC inverter fans, you need to test them without a megger, test the diodes in the motors.
    Last edited by paul_h; 30-04-2008 at 02:38 PM.

  6. #6
    Join Date
    Aug 2006
    Location
    Southend on Sea
    Posts
    6
    Rep Power
    0

    Re: Daikin Compressor failure

    Thanks for the tips i have the dealer going to site tomorrow to inspect the unit, would a normal continuity meter show up the windings as down to earth or does it have to be a meggar?

    Regards Mark

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin Compressor failure

    Quote Originally Posted by Wof56 View Post
    Thanks for the tips i have the dealer going to site tomorrow to inspect the unit, would a normal continuity meter show up the windings as down to earth or does it have to be a meggar?

    Regards Mark
    It has to be mega Ohm meter! Normal meter don't have voltage high enough to measure insulation strength which is different at different voltage. You maybe could measure some resistance with normal meter depending on damage to insulation but that measurement is not correct.
    Last edited by nike123; 01-05-2008 at 01:15 PM.

Similar Threads

  1. Service checker Daikin
    By Cool100 in forum Air Conditioning
    Replies: 26
    Last Post: 22-03-2011, 12:53 PM
  2. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  3. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •