    compressor higher than condenser



    hello to everybody...
    i am new in this site and i would appreciate your help ..my company install refrigerators in supermarket and i want to ask if it is possible the condenser to be in a lower level than the multi of compressors? if yes what we have to take care? we have any high difference limit? what possible problems we can face?
    thanks in advance for your help



  2. #2
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: compressor higher than condenser

    it doesn't really matter if the condenser is lower than the compressors, what matters (in my opinion - I have seen others claim to have no issues) is that the condenser is above the liquid reciever, this will ensure your condenser drains consistently and doesn't surge the liquid levels in your reciever or log in the condenser. I have found it most beneficial to locate the reciever under the condenser if the condenser is going to be lower than it, you can still run the main liquid line back to the plant room to distribute the refrig in a header.
    ...and she said "give it to me you big fridgie"

  3. #3
    Join Date
    Apr 2008
    Location
    philippines
    Posts
    95
    Rep Power
    17

    Re: compressor higher than condenser

    what kind of ref? walk in chiller or just a simple ref? is it split or not?

    if split please consider this;

    *check maximum line set length as per manufacturer

    if you installed it the unit must have a proper oil return. "IF A LINE SET HAS A RISE FOLLOWED BY A DROP, ANOTHER RISE CANNOT BE MADE. LIKEWISE, IF A LINE SET HAS A DROP FOLLOWED BY A RISE, ANOTHER DROP CANNOT BE MADE."

    MAXIMUM LINE SET DISTANCE FORMULA:
    1) measured rise___X1.7=___calculated rise
    2) measured drop___X6.6=___calculated drop
    3) measured horizontal distance=____horizontal distance
    4) total calculated distance=____total calculated distance (just add calculated rise + calculated drop + horizontal distance)

    hope this one helps...

    _____________________________________________
    brian
    SAMSUNG Tech. Support

Similar Threads

  1. Condensor split temperature
    By Peter_1 in forum Fundamentals
    Replies: 14
    Last Post: 31-07-2011, 05:49 PM
  2. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  3. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM
  4. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM
  5. Condenser Fan
    By Vicky in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 20-04-2005, 08:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •