    I am trying to start our chiller York Millennium model YTG0A3B2-CGJ and find that the oil sump tempurature is not increasing to setpoint 125 it stay same around 70 any suggestion for troubleshooting the problem.

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Oil sump temperature

    Check that the sump / Crankcase oil heater is working.
    Also it is quite common where fitted to have the MCB supplying the heater fail.
    Or if relevant its Cartridge Fuse blow.
    In short my first suggestion would be that the relevant supply has been interrupted.
    Secondly the heater may be U.S.
    If necessary use a clamp meter to confirm!
    Cheers Grizzly
    Sorry the above is not strictly correct as a YT is a centrif!
    I will get back with more once the archives have been consulted but the bulk may still be relevant!!!!
    Last edited by Grizzly; 28-04-2008 at 11:38 PM. Reason: I got my models mixed up.

  3. #3
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Oil sump temperature

    Quote Originally Posted by msatali View Post
    I am trying to start our chiller York Millennium model YTG0A3B2-CGJ and find that the oil sump tempurature is not increasing to setpoint 125 it stay same around 70 any suggestion for troubleshooting the problem.

    Thanks
    Hi msatali, First of all is the oil temperature controller working it sounds like its faulty, if you haven`t already checked it thats the place to start. By the way is the ambient temp 70 then it might be the oil heater

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 01:43 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •